You need to test from the electrical system grounding electrode to "remote earth", often defined as being at least 50' from any grounding electrode or metallic object that is connected to the electrical grounding system. This will typically show a small voltage. Then test the pool equipment and water to the same remote earth point. The voltages from both sets of tests should be the same. Note that loading in the building and on the system may change based on changing load conditions.