So you are using an external tester?
Yes, a GFCI plug tester which doesn't work in this situation
So you are using an external tester?
Sorry, I misunderstood, thought you meant the test button on the plug tester
Good idea about using a different test method. The resistance of a light bulb would do the trick. I just was not expecting the GFCI to be slower than the breaker. I am going to try to find the trip times for each.
I am currently working in an older home with ungrounded 2 wire circuits. I have installed a GFCI receptacle to protect 3 wire ungrounded receptacles downstream. I know that a plug tester with a GFCI test button will not trip the GFCI receptacle but I assumed I could test the downstream receptacles by shorting the hot side of the receptacle to a nearby piece of grounded metal. I thought that it would simply trip the upstream GFCI well before the breaker would trip. To my suprise, I got a nice flash and the breaker tripped. Aside from any criticisms of my test methods, can anyone tell me why the breaker tripped instead of the GFCI? I am pretty sure that everything is connected properly. The test button on the GFCI works and kills power to the downstream receptacles.
Thanks for any help.
None of the GFCI device directions will tell you to use an external tester of any sort. One of the reasons for this is that external testers will not work on a two wire circuit.
There is no need of that.
The accepted method is to put a load in at the downstream receptacle and push the trip button at the GFCI device.
If this is some hobby type exercise at your house that is great but if you are doing this on the job the tests you are describing will not count for anything if comes down to that.
Nothing you cobble together will be looked at as a reliable test.
The manufacturers testing instructions can fall short IMO. The GFCI can be miswired and still pass the suggested test method. I think it is important to think about what we are doing and if necessary go beyond what is recommended.
I agree with the test method that you have suggested however that may not be the recommended test method per the manufacturers instructions.
Testing GFCI receptacles on the job does not require any special testing equipment.
I understand that the tester I described is not a professional tool. Please don't imply that I am a cobbler. There are cases in which I have fabricated lab quality test instruments where required by my customer.
I don't think the GFCI is faster. The trip time for a GFCI is often stated at 1/4 second. That is 15 cycles and a breaker can clear a short much faster than that.The GFCI should be faster, yes. You never gave the GFCI a chance to see any imbalance between the hot and neutral going to ground. You left the neutral out of the circuit.
The UL standard would permit the trip time to be 0.78 seconds for that load.The GFCI should trip within 25ms on a 500ohm fault.
The formula for a UL Listed Class A GFCI is:Thanks all for your input. I will post back if I find any conclusive info on GFCI reaction time vs. breaker.
Many people are amazed at how fast circuit breakers actually are, when tripping in their instantaneous region, like with a direct short.
Likewise, many are surprised that GFCI's actually have a time delay in their operation.
I don't think the GFCI is faster. The trip time for a GFCI is often stated at 1/4 second. That is 15 cycles and a breaker can clear a short much faster than that.
Thank you to you both for the clarification. I think it is safe to say that if you want to test GFCI circuitry a dead short to ground is not the way to do it.
I did that in the past also....while the GCFI will limit the duration of the fault, it does not limit the current that flows into the fault.Yeah, when I was getting started I figured it would not be a spark over 7ma if shorted. My screwdriver suffered the consequences and I learned things do not open before the sparks fly. :dunce:
That formula implies the GFCI is supposed to open in under 19.7 ms when the imbalance is 300 mA or more (e.g. the OP's dead short). Apparently the instantaneous trip on a circuit breaker can be faster than that?The formula for a UL Listed Class A GFCI is:
T=seconds, I=mA of current.
I believe 300mA is the upper limit for the formula, larger currents will not produce faster times.
One time trip curve that I looked at shows the instantaneous trip time to be between 1/2 and 1 cycle, so less than 16.6 ms.That formula implies the GFCI is supposed to open in under 19.7 ms when the imbalance is 300 mA or more (e.g. the OP's dead short). Apparently the instantaneous trip on a circuit breaker can be faster than that?
Cheers, Wayne
If I press the test button on the GFCI and the load shuts down what miswire are you thinking of?
The method I described is recommend by the manufacturers and the CSPC
That seems a lot longer then I would expect. How is that derived?The UL standard would permit the trip time to be 0.78 seconds for that load.
I think it is a common misconception that a human will only be exposed to 6mA since that is the trip threshold of a GFCI. In fact it could be much more for a finite amount of time.I did that in the past also....while the GCFI will limit the duration of the fault, it does not limit the current that flows into the fault.
The method you are describing should catch a miswire. This is not however the test that is recommended by Leviton for example. See here. It is possible to miswire and the prescribed test would not catch it. I should not test any further however because of 110.3(B)
(c) If you installed your GFCI using step 7B press the TEST button, then plug
a lamp or radio into surrounding receptacles to see which one(s), in
addition to the GFCI, lost power when you pressed the TEST button. DO
NOT plug life saving devices into any of the receptacles that lost power.
Place a "GFCI PROTECTED OUTLET" sticker on every receptacle that
lost power, then press the RESET button to reset the GFCI.
One time trip curve that I looked at shows the instantaneous trip time to be between 1/2 and 1 cycle, so less than 16.6 ms.
See this UL articleI thought it was >6mA? What you are saying is not incorrect since 7>6. I thought anything over 6mA and the GFCI should trip.