We have recently formed a new group in our refinery to conduct medium & high voltage (35kV) switching. Pre-Katrina this duty was contracted third party. The switching will now be conducted by inhouse personnel. We are in the process of purchasing flash suits, gloves, blankets, etc.
Please direct me to the section in NFPA 70E showing the frequency (number of months) required for the testing of gloves, blankets, etc.
Under 250.2 (A), it states; visual before each use with intervals not to exceed one year. (B) states; testing shall not exceed 3 years.
I have heard (smoke pen gossip) 6 months is required, but I can't find this info.
Thanks for your help in advance.
Southeast Louisiana
Please direct me to the section in NFPA 70E showing the frequency (number of months) required for the testing of gloves, blankets, etc.
Under 250.2 (A), it states; visual before each use with intervals not to exceed one year. (B) states; testing shall not exceed 3 years.
I have heard (smoke pen gossip) 6 months is required, but I can't find this info.