the question read....Calculate the demand for the fastened in place appliances.
Water Heater 1500VA
Garage door opener 960VA
Dishwasher 960VA(assume 50% motor load)
Garbage disposal 1240VA
Do you add the loads and then calculate the demand or do you need to take into consideration the motor loads of the disposal, garage door and dishwasher. Do you apply article 430 to the motor loads and then add the loads?
Question 2:
120V X 20 A = 2400VA 2400VA * 180VA ?= 13 receptacles per circuit. So why do a lot electricians think 7 receptacles is the maximum allowed on one circuit.
Water Heater 1500VA
Garage door opener 960VA
Dishwasher 960VA(assume 50% motor load)
Garbage disposal 1240VA
Do you add the loads and then calculate the demand or do you need to take into consideration the motor loads of the disposal, garage door and dishwasher. Do you apply article 430 to the motor loads and then add the loads?
Question 2:
120V X 20 A = 2400VA 2400VA * 180VA ?= 13 receptacles per circuit. So why do a lot electricians think 7 receptacles is the maximum allowed on one circuit.