Hello all. Got a question. I am wiring an office building for a family member's used car lot. The building was a two story split level residential home with a basement that is being converted to an office.
My question is, can I use romex in this building?
The NEC is a little confusing saying that it's permitted in type 3,4,5 buildings (Other structures permitted to be of Types III, IV, and V construction except as prohibited in 334.12.) but 334.12 states :
(A) Types NM and NMC. Types NM and NMC cables shall not be used as follows:
(1) In any dwelling or structure not specifically permitted in 334.10(1), (2), (3), and (5).
(2) Exposed within a dropped or suspended ceiling cavity in other than one- and two-family and multifamily dwellings.
(3) As service-entrance cable.
(4) In commercial garages having hazardous (classified) locations as defined in 511.3.
(5) In theaters and similar locations, except where permitted in 518.4(B).
(6) In motion picture studios.
(7) In storage battery rooms.
(8) In hoistways or on elevators or escalators.
(9) Embedded in poured cement, concrete, or aggregate.
(10) In hazardous (classified) locations, except where specifically permitted by other articles in this Code.
(11) In hotels, motels, commercial, mercantile, industrial, institutional, and public buildings.
(B) Type NM. Type NM cable shall not be used as follows:
(1) Where exposed to corrosive fumes or vapors.
(2) Where embedded in masonry, concrete, adobe, fill, or plaster.
(3) In a shallow chase in masonry, concrete, or adobe and covered with plaster, adobe, or similar finish.
(4) In wet or damp locations.
It looks to me like Romex is NOT permitted in this building CAN SOMEONE VERIFY THIS??
THANKS FOR ALL YOUR HELP IN ADVANCE.
My question is, can I use romex in this building?
The NEC is a little confusing saying that it's permitted in type 3,4,5 buildings (Other structures permitted to be of Types III, IV, and V construction except as prohibited in 334.12.) but 334.12 states :
(A) Types NM and NMC. Types NM and NMC cables shall not be used as follows:
(1) In any dwelling or structure not specifically permitted in 334.10(1), (2), (3), and (5).
(2) Exposed within a dropped or suspended ceiling cavity in other than one- and two-family and multifamily dwellings.
(3) As service-entrance cable.
(4) In commercial garages having hazardous (classified) locations as defined in 511.3.
(5) In theaters and similar locations, except where permitted in 518.4(B).
(6) In motion picture studios.
(7) In storage battery rooms.
(8) In hoistways or on elevators or escalators.
(9) Embedded in poured cement, concrete, or aggregate.
(10) In hazardous (classified) locations, except where specifically permitted by other articles in this Code.
(11) In hotels, motels, commercial, mercantile, industrial, institutional, and public buildings.
(B) Type NM. Type NM cable shall not be used as follows:
(1) Where exposed to corrosive fumes or vapors.
(2) Where embedded in masonry, concrete, adobe, fill, or plaster.
(3) In a shallow chase in masonry, concrete, or adobe and covered with plaster, adobe, or similar finish.
(4) In wet or damp locations.
It looks to me like Romex is NOT permitted in this building CAN SOMEONE VERIFY THIS??
THANKS FOR ALL YOUR HELP IN ADVANCE.