The only hope left is to get states to amend the AFCI rules out of their adopted codes.
If enough locals speak up its possible.
The only hope left is to get states to amend the AFCI rules out of their adopted codes.
Electricians need to understand the functionality of afci technology
Not the manufacturers pitch
Not any CMP substantiation
Not any canned NRTL study
Not any nema members opinion
~RJ~
I suggest everyone who has 10 minutes to spare go to http://www.nfpa.org/codes-and-standards/document-information-pages?mode=code&code=70&tab=editions and submit a revision 210-12 Arc-fault protection. The 2017 revision now removes the specific areas where afcis are required and simply says ALL 15 and 20amp 120v outlets are to be afci protected. Maybe if there original intent was to detect frayed or damaged cords then we should get rid of circuit afci requirements and have manufacturers integrate afci tech into all new plug in equipment so that the equipment itself will trip. This way the line side of the circuit will not be affected only the affected equipment. I did not use that suggestion in my submittal but should have. Maybe if more of us submit revisions to get rid of these things, at least until the tech is perfected, they will take it more seriously. Im sure getting rid of afci's is a pipe dream because of the BIG MONEY involved, but if we don't at least try for change than all of our talk is just that.
I guess I'm the only one who doesn't have a problem with AFCI's :? Seriously, I haven't had any issues with them. They catch sloppy wiring, and other mistakes...:roll: My vacuum doesn't trip the Square D Homeline AFCI's i have at my house. Can someone give more specific details on the issues?
I have had two occasions where power tools that had soft start circuitry would trip an AFCI every time, GE and Homeline breakers.I guess I'm the only one who doesn't have a problem with AFCI's :? Seriously, I haven't had any issues with them. They catch sloppy wiring, and other mistakes...:roll: My vacuum doesn't trip the Square D Homeline AFCI's i have at my house. Can someone give more specific details on the issues?
There is no evidence that self sustaining series arcs can even exist at dwelling unit voltages.Series arcs occur in residential wiring.
Chris
b. The maximum length of the branch-circuit wiring
from the branch-circuit overcurrent device to the
first outlet shall not exceed 15.2 m (50 ft) for a
14 AWG conductor or 21.3 m (70 ft) for a ]2 AWG
conductor.
210.12(A)(3)b presents with values that hint at an afci's only viable function
these values are not arbitrary ....
~RJ~
The UL report states “breakers can be effective at mitigating arcing faults,
provided the available fault current can be guaranteed to exceed the magnetic
trip level of the circuit breaker by a factor of 1.25.”
(b)The branch circuit breaker shall be listed and marked as having an
instantaneous trip not exceeding 300 amperes.
This proposal establishes a circuit breaker
listing and marking requirement for the magnetic trip level at or below 300A in
order to ensure the breaker will protect the circuit from a parallel arcing fault
when at least 500A of available fault current is present as required in the first
parameter.
LAROCCA, R.: While we support the panel action, continued support is
dependent upon review of additional data that would confirm the availability of
sufficient short circuit current capability at the panel of a typical installation.
The arc fault protection of the branch circuit will be provided by a system
that includes an outlet branch circuit AFCI, a circuit breaker having a known
instantaneous trip current and a branch circuit of a limited length and resistance
to ensure that the fault current is sufficient to trip the breaker during a parallel
arcing fault at the installation point of the outlet branch circuit AFCI. The latest
UL Research Report takes into consideration the impact of the available current
at the panel on the acceptable length of the branch circuit home run to the first
outlet. Calculation shows that as the available current at the origin of the
branch circuit varies, so does the allowable length of the home run.
Additional study is needed to provide data regarding the current available at
the origin of the branch circuit in a typical installation. From this data, the
panel will be able to determine if modification of the panel action should be
considered at the ROC.
The report focused on providing data on the performance of conventional
circuit breakers with respect to arc faults in the home run portion of the branch
circuit and identified the parameters that must be met and controlled for this to
happen.
As long as these parameters are controlled, it can be concluded that an outlet
branch circuit type arc-fault circuit interrupter could possibly be used in
conjunction with a low-magnetic type circuit breaker to protect the branch
circuit. The critical parameters summarized in the report include: a minimum
available fault current, a maximum magnetic trip level for the circuit breaker,
impedance of the conductor, the actual voltage and the length of the conductor.
This proposal is based on utilizing the parameters set forth by the UL Report
to revise 210.12 to permit using an outlet branch circuit arc-fault circuit
interrupter in conjunction with a low magnetic trip circuit breaker.
(2) A listed outlet branch circuit type arc-fault circuit interrupter installed at
the first outlet on the branch circuit where all of the following conditions are
met:
(a) The branch circuit over current protection device shall be a listed circuit
breaker having an instantaneous trip not exceeding 300 amperes.
(2) A listed outlet branch circuit type arc-fault circuit interrupter installed at the
first outlet on the branch circuit where all of the following conditions are met :
(a) The available fault current at the branch circuit overcurrent device shall not
be less than 500A and the ambient temperature shall not be less than 20°C
(68°F).
(b)The branch circuit breaker shall be listed and marked as having an
instantaneous trip not exceeding 300 amperes.
© The branch circuit wiring shall be continuous from the branch circuit
overcurrent device to the outlet branch circuit arc-fault circuit interrupter.
(d) The maximum length of the branch circuit wiring from the branch circuit
overcurrent device to the first outlet shall be determined using the following:
L = (0.4×Vrms) / (1.25×300×pL)
L is the maximum length of the “home run” in feet;
pL is the resistivity per unit foot of each conductor of the NM cable gauge
being used; and
Vrms is the actual supply voltage.
Echo's IEC standards....even CMP-2 gets this!
so an AFCI is essentially an Americanized RCD
Why not simply mandate toroidal coils of descending magnitude , and spare us all the faux arc marketing ?
~RJ~
my theory cup runneth over Mbrooke
~RJ~