masterinbama
Senior Member
- Location
- Huntsville Alabama
Went to do a job for a good customer of mine. She was selling her house and the buyers inspector cited some electrical issues,most of which he was right on. The house has a 400 amp service back to back in the garage with proper bonding and grounding. From there a 100 amp feeder goes to the pool house panel with no bonded metallic items between them. 100 amp panel in pool house has 2 ground rods driven with a #4 ground wire and neutral and grounds bonded. From this panel a 40 amp feeder goes to a motor home garage. This panel was not grounded and bonded so i bonded it and drove 2 rods. Inspector stated that " at no point past the service entrance can neutrals and grounds be connected on the same bus. I quoted 250.32 exception (2) and he still refuses to turn this house loose for closing. The sellers real estate agent agrees with me and we basically told the home inspector he needed to go buy a code book.