Prospex

Member
Typically, in modern kitchen designs, the floor plan includes a space specifically intended for a refrigerator. In fact, such designs preclude installing a refrigerator anywhere else without remodeling the kitchen. Thus, the space is intended as a "dedicated space" for a refrigerator, both by design and use. However, unlike the exception for non-GFCI protected wall outlets in garages, the term "dedicated space" is not used for any part of the exceptions pertaining to non-GFCI protected wall outlets in kitchens.

The requirement for GFCI protection of kitchen outlets applies to outlets serving countertops. It seems that once a refrigerator is in place, the outlet in the space for the refrigerator would be inaccessible for any other use. The NEC requirement for GFCI protection of outlets only applies to outlets which serve countertops and the exception to GFCI protection also applies to outlets for food waste disposers, dishwashers, and trash compactors - outlets typically located inside and near the back of kitchen base cabinets.

The exception for a kitchen wall outlet in a space designed and intended for a refrigerator would seem to imply (without using the term "dedicated space") that, like the exception for garages, the non-GFCI protected outlet intended for the refrigerator is, in fact, serving a dedicated space because that space is intended for nothing other than a refrigerator, an appliance that "is not easily moved form one place to another and that is cord-and-plug connected."

In addition, most kitchen wall outlets in such spaces designed and intended for a refrigerator are less than six feet from a countertop. Since there is no requirement that a refrigerator be installed or that, if one is installed, it will prevent ready access to the outlet, the outlet could potentially "serve a countertop." Does anybody know why the NEC doesn't include the term and concept of "dedicated space" with regard to the exception for this specific kitchen wall outlet?

Just curious
 
I use the receptacle that my refrig is plugged into for a Bose radio, phone charger and some other junk. I would guess is that the NEC regards the receptacle as not likely to be used to serve counter top loads. But from my example that clearly isn't always the case.
 
210.8(A)(6) specifies the requiremet for GFCI protected receptacles in kitchens. GFCI protection is required only where "the receptacles are installed to serve the countertop surfaces".

210.52(C)(5) explicitly requires the receptacles serving countertops to "be located above, but not more than 500 mm (20 in.) above, the countertop".

If the receptacle is not located within 20 inches above the countertop, it doesn't require GFCI protection.

The possibility that you may plug a countertop appliance into the "refrigerator" receptacle has no bearing on whether or not the Code requires it to be GFCI Protected.

Consequently, a reference to a dedicated space is not required since all of the spaces that a normal refrigerator could be located are excepted from the requirement for GFCI protection.
 
So lets say that the receptacle for the refrig is mounted at 45" and is 6" from the edge of the countertop, but in the space for the refrig. Is it possible that the receptacle still could serve the countertop?
 
infinity said:
So lets say that the receptacle for the refrig is mounted at 45" and is 6" from the edge of the countertop, but in the space for the refrig. Is it possible that the receptacle still could serve the countertop?
It is not above the countertop, and therfore, is not among those that the code requires to be GFCI protected.
 