Let's all keep in mind that the only reason we can have a scenario where the wire is sized smaller that the breaker is because the motor has built in thermal overloads. If a motor does not have those, then you need to install them. And the upstream breaker (which is only used for short circuit and ground fault, now) is sized higher in order to prevent nuisance tripping on startup, since startup current can be 6 to 8 times higher than steady state.
As an academic exercise, I'm thinking that you could potentially even use a molded case switch as your upstream protection, since it also has built-in magnetic/instantaneous protection. The thermal part of the breaker is not used.
Also note that in Article 440, the value of the OCPD is limited to 225% of the motor FLA. The gap is wider for generic Article 430 motors.