Can someone explain this to me?
If reactive power isn't power, why does it take more power at the generating end to deal with it? To me, that seems like a violation of the law of conservation of energy.
If reactive power just oscillated to and fro, wouldn't the result be 'nothing' to the 'eye' of the generating end?
I am probably overlooking something that to the rest of you is obvious.....
I would not say that it is obvious, but I will try to explain it simply:
1. The prime mover of the generator (steam or gas turbine, diesel, etc.) needs to be able to deliver enough power to keep the generator shaft turning at the regulated design speed. To do this it ONLY has to be able to produce power to match the "real" power consumed by the loads and the sum of the losses in the distribution network. (If the generator is three phase, then for balanced loads of matching PF the prime mover will see a constant torque load, regardless of whether there is reactive power flowing out and back at different times in the cycle.)
2. Adding in loads with low PF increases the current that the generator must deliver, and so increases the distribution network losses in the same proportion. To that extent the prime mover must be able to deliver more power, but this is not nearly in direct proportion to the apparent power.
3. The generator itself (windings, etc) must be able to deliver the current to match the apparent power, even if this does not show up as a load on the prime mover. To deliver this additional current the generator needs to be more heavily built than it would be if it only had to deal with the real power.
4. An additional consideration is that the generator output must be regulated to match the needs of the grid, including maintaining output voltage or even increasing it to deal with generator and distribution network losses. This regulator is a feedback loop and under some conditions of out of phase current and voltage the regulator may not be stable. To that extent delivering a large amount of reactive power will stress the design and operating parameters of the generator itself, again independent of the prime mover.
If that does not answer your question, please let me know what parts are still giving you problems.