Re: The requirement of 2002 NEC 517.33 for hemodialysis room
Steve,
I agree that we review each on a case-by-case basis.
My fellow Electrical Plans Examiner, Gary, has made a point that 517.25, which defines the scope of part III of Article 517, includes outpatient facilities, & other health care facilities in it's description of facilities that are required to have essential electrical systems. 517.30 goes on to specify Hospitals, but I still don't think that this limits 517.33 only to hospitals. In addition, 517.33 specifies that task illumination and selected receptacles for the mentioned occupancies. The back-up batteries for the hemodialysis units would not back up task lighting and other receptacles that may need additional power back-up. We've forwarded this discussion to our Chief Electrical Inspector, who is the AHJ for our City, for a ruling.
Thanks again.