See post #68.On the contrary suppose your load requirements would grow from present design load of 400 KVA to beyond but within 800 KVA in near future,would you buy 400 KVA transformer or 800 KVA transformer?
See post #68.On the contrary suppose your load requirements would grow from present design load of 400 KVA to beyond but within 800 KVA in near future,would you buy 400 KVA transformer or 800 KVA transformer?
The simple point I was making is that the notion of over rating a transformer to obtain better efficiency, as you have suggested simply, doesn't hold water.It is.Spare capacity is a concept of modern electrical design.
It will do in relation to load growth.The simple point I was making is that the notion of over rating a transformer to obtain better efficiency, as you have suggested simply, doesn't hold water.
Yes.Do not load it fully,if you do not have protective relays that would trip the transformer to prevent its loss of service life should its hot spot temperature rises above a certain limit.In the absence of such protective relays,you may safely load the transformer to 80% of its capacity.
That is just a design choice.
It is not a design choice.:dunce:
Spare capacity is a concept of modern electrical design.
I understand the point you're making. Operation on no load has the least losses. But not the best efficiency. In fact, at that point it's zero. Power in and no power out.0 load: 3960.7 = 1.00%
1/2 load: 3960.7+1160.2= 1.28%
3/4 load: 3960.7+2610.4= 1.64%
full load: 8597.6/400000= 2.15%
By gosh the efficiency IS a lot less at lower loads. But someone PLEASE tell me what significance this has to the use of a transformer? By this reckoning, we should use ALL transformers at their most "efficient" point: 0% load!
May be misleading.See post#55.......the efficiency.........is best at rated load....
Were you mislead?May be misleading.See post#55.
Sorry,yes.Are my figures wrong?
OK.
Post the corrected figures then.
I understand the point you're making. Operation on no load has the least losses. But not the best efficiency. In fact, at that point it's zero. Power in and no power out.
I hope you don't mind that I've calculated efficiencies based on your figures:
![]()
What it shows is that the efficiency doesn't vary very much with load over the likely operating range and is best at rated load thus negating the argument that operating below full load rating delivers better operating efficiency.
to follow up on this, what DOES happen if you use a double size xfmr to make it "more efficient?" If one adds the actual WATTS losses, they will see this more efficient xfmr actually is LESS efficient at 1/2 load would he not? 1.28% of 800kva= 10,240watts loss........ 2.15% above is 8597.6watts loss on the 400kva transformer for the same load? Which is "MORE" efficient?
efficiency is power out/power in (tnx for pointing out typo) so just to state a transformers different load points by itself is silly.
where u said 2pc 1000kva xfmrs loaded to 50% each is more efficient than 1pc loaded to 100%, Unless u can provide core and cu losses to back up that particular comment. I know we can design transformers to trade losses between core and cu as needed so do not come back with a different design 100kva for the single use model - all must be the same for valid comparison. If u give design proof showing better power out/power in here I will ask our transformer design wizards to check your math.May be misleading.See post#55.
Excellent analysis showing the OVERALL power out/ power in efficiency IS better loaded higher.
This was my in post 50:
Sorry TM, but this seems to contradict your post pointing to a post that pointed to another post that pointed to another:
where u said 2pc 1000kva xfmrs loaded to 50% each is more efficient than 1pc loaded to 100%, Unless u can provide core and cu losses to back up that particular comment. I know we can design transformers to trade losses between core and cu as needed so do not come back with a different design 100kva for the single use model - all must be the same for valid comparison. If u give design proof showing better power out/power in here I will ask our transformer design wizards to check your math.
That was what I was trying to state: effy by itself of the transformer is a micro picture; the macro picture is the overall power out/ power in - in which case probably most times a transformer loaded less than 100% will be less efficient than a larger transformer at a given load.
I feel arguing with you about this is beating a dead horse TM, but the OP was asking about % transformer load.
OK.
Post the corrected figures then.
Seems like a reasonable request.
No it isn't.It is in post#82,please.
Were you mislead?
Are my figures wrong?
Sorry,yes.
Post the corrected figures then.
First recheck your calculations.The efficiency at 100% loading is 400/(400+0.85976) =400/400.85976=99.7855% and not 97.85%.No it isn't.
My post #77
Your post #78
My post #79
OK.
Here are the figures again:
![]()
You claimed that my figures were wrong.
I made a reasonable request that you post corrected figures.
Care to do so now?
99.7855%!!!!!First recheck your calculations.The efficiency at 100% loading is 400/(400+0.85976) =400/400.85976=99.7855% and not 97.85%.
And here's the curve of how efficiency varies with loading:First recheck your calculations.The efficiency at 100% loading is 400/(400+0.85976) =400/400.85976=99.7855% and not 97.85%.
How?Put up the formula for efficiency.99.7855%!!!!!
that's wrong.
First recheck your calculations.The efficiency at 100% loading is 400/(400+0.85976) =400/400.85976=99.7855% and not 97.85%.