The use of a disconnect as a raceway.

Status
Not open for further replies.
What I have is a disconnect outside of a building that feeds a condensor unit. The disconnect is fed with a 3/4" conduit. Can I pull a branch circuit in with the feeders (fed from same source) and pipe to a weatherproof GFCI below the disconnect?
 
What I have is a disconnect outside of a building that feeds a condensor unit. The disconnect is fed with a 3/4" conduit. Can I pull a branch circuit in with the feeders (fed from same source) and pipe to a weatherproof GFCI below the disconnect?

I agree with the others but also want to point out that once you apply the required derating the feeder conductors will likely be to small.
 