The use of EMT as a service mast

Status
Not open for further replies.

randyheggem

New User
Location
Minnesota
Occupation
Electrician
Where exactly in the NEC does it explicitly say you cannot use EMT as a service mast? 230.28 only speaks to being of adequate strength or be supported by braces to withstand the strain. It doesn't say specifically no EMT. I cannot find a code article listing approved wiring methods for service masts. 230.3.B is only applicable for underground service conductors. In 358.12 for EMT uses not permitted it says nothing of service masts. I know according to my internet searches EMT cannot handle the high levels of fault current which could fall under 358.12.1 but that isn't very specific and subjective due to the fact RMC cannot withstand the levels of fault current either and RMC is able to be used as a service mast. Is it written in the MN residential building code somewhere or do the manufactures of EMT state their product will not work for use as a service mast?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The power company will also determine that emt isn't strong enough.

230.28 Service Masts as Supports. Only power service-drop or
overhead service conductors shall be permitted to be attached
to a service mast. Service masts used for the support of servicedrop
or overhead service conductors shall be installed in
accordance with 230.28(A) and (B).
(A) Strength. The service mast shall be of adequate strength
or be supported by braces or guys to withstand safely the strain
imposed by the service-drop or overhead service conductors.

Hubs intended for use with a conduit that serves as a service
mast shall be identified for use with service-entrance equipment.
(B) Attachment. Service-drop or overhead service conductors
shall not be attached to a service mast between a weatherhead
or the end of the conduit and a coupling, where the coupling
is located above the last point of securement to the building or
other structure or is located above the building or other structure.
 

jap

Senior Member
Occupation
Electrician
Are the service conductors actually attaching to the mast?

JAP>
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Are the service conductors actually attaching to the mast?

JAP>
Many times yes and even if not it's as Bill says, the POCO conductors might and they can dictate what they want.
 

jap

Senior Member
Occupation
Electrician
Many times yes and even if not it's as Bill says, the POCO conductors might and they can dictate what they want.

I meant EMT may be acceptable as a service mast as long as it is not being used as a means of support for the service conductors.

JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I meant EMT may be acceptable as a service mast as long as it is not being used as a means of support for the service conductors.

JAP>
What is the actual definition of a mast? Isn't it the service raceway that also supports the drop? If the drop isn't supported by the raceway is it still a mast?
 

jap

Senior Member
Occupation
Electrician
What is the actual definition of a mast? Isn't it the service raceway that also supports the drop? If the drop isn't supported by the raceway is it still a mast?

Not sure,,,, is a mast on a sailboat not a mast if the sails aren't raised?

JAP>
 

jap

Senior Member
Occupation
Electrician
The rule says that only power service-drop or over head service conductors are permitted to be attached to a "Service Mast"
Then goes on to explain how to be installed if used as a means of support.

Therefore a service mast is considered a "Mast" before anything is ever attached to it.

At least that's the way I see it.

Jap>


230.28 Service Masts as Supports. Only power service-drop or
overhead service conductors shall be permitted to be attached
to a service mast
. Service masts used for the support of servicedrop
or overhead service conductors shall be installed in
accordance with 230.28(A) and (B).
(A) Strength. The service mast shall be of adequate strength
or be supported by braces or guys to withstand safely the strain
imposed by the service-drop or overhead service conductors.

Hubs intended for use with a conduit that serves as a service
mast shall be identified for use with service-entrance equipment.
(B) Attachment. Service-drop or overhead service conductors
shall not be attached to a service mast between a weatherhead
or the end of the conduit and a coupling, where the coupling
is located above the last point of securement to the building or
other structure or is located above the building or other structure.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
The rule says that only power service-drop or over head service conductors are permitted to be attached to a "Service Mast"
Then goes on to explain how to be installed if used as a means of support.

Therefore a service mast is considered a "Mast" before anything is ever attached to it.

At least that's the way I see it.

Jap>


230.28 Service Masts as Supports. Only power service-drop or
overhead service conductors shall be permitted to be attached
to a service mast
. Service masts used for the support of servicedrop
or overhead service conductors shall be installed in
accordance with 230.28(A) and (B).
(A) Strength. The service mast shall be of adequate strength
or be supported by braces or guys to withstand safely the strain
imposed by the service-drop or overhead service conductors.

Hubs intended for use with a conduit that serves as a service
mast shall be identified for use with service-entrance equipment.
(B) Attachment. Service-drop or overhead service conductors
shall not be attached to a service mast between a weatherhead
or the end of the conduit and a coupling, where the coupling
is located above the last point of securement to the building or
other structure or is located above the building or other structure.
What would a drop be supported by if it isn't supported by the mast? What other function would a mast serve?
 

jap

Senior Member
Occupation
Electrician
What would a drop be supported by if it isn't supported by the mast? What other function would a mast serve?

An eave of a house,,,, an anchor into a Pole,,,, anywhere where it's not actually attached to the "mast" or "riser" or whatever one wants to call it.


JAP>
 
Last edited:

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
In California, Southern California Edison only allows rigid steel or IMC conduit for risers when attaching service drops.
 

Attachments

  • SCE - Electrical Service Requirements - Overhead.jpg
    SCE - Electrical Service Requirements - Overhead.jpg
    227.2 KB · Views: 34
  • Electrical Service Requirements - LB.jpg
    Electrical Service Requirements - LB.jpg
    163.5 KB · Views: 39

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
An eave of a house,,,, an anchor into a Pole,,,, anywhere where it's not actually attached to the "mast" or "riser" or whatever one wants to call it.


JAP>
This was how the service was connected on my last house. The town inspector said I had to put a mast in before closing on the sale, because that type of connection was not allowed.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
What is the actual definition of a mast? Isn't it the service raceway that also supports the drop? If the drop isn't supported by the raceway is it still a mast?

I was thinking that the nec may need a definition to clarify for some people. Imo. the mast is the raceway that rises above the rooftop- usually thru the overhang of the building - that gives the power company's a place to attach the service drop. That is why the power company determines if the conduit is strong enough. In a residence of 200 amps 2" rmc is the standard around here and I have seen it get bent to a 45 degree angle when a tree falls on the overhead lines. Obviously the higher you go above the roof the weaker the conduit and hence the need for a tie down

looking at the definition of mast in the dictionary you can see the similarities between a ship's mast and the electrical mast.
Definition of mast
The meaning of MAST is a long pole or spar rising from the keel or deck of a ship and supporting the yards, booms, and rigging.

The riser is the raceway that does not go above the roof and doesn't support the overhead conductors.
 

jap

Senior Member
Occupation
Electrician
This was how the service was connected on my last house. The town inspector said I had to put a mast in before closing on the sale, because that type of connection was not allowed.

It's still allowed depending on your area.

JAP>
 

jap

Senior Member
Occupation
Electrician
I was thinking that the nec may need a definition to clarify for some people. Imo. the mast is the raceway that rises above the rooftop- usually thru the overhang of the building - that gives the power company's a place to attach the service drop. That is why the power company determines if the conduit is strong enough. In a residence of 200 amps 2" rmc is the standard around here and I have seen it get bent to a 45 degree angle when a tree falls on the overhead lines. Obviously the higher you go above the roof the weaker the conduit and hence the need for a tie down

looking at the definition of mast in the dictionary you can see the similarities between a ship's mast and the electrical mast.


The riser is the raceway that does not go above the roof and doesn't support the overhead conductors.

Yes, that's the a mast, but, it doesn't have to have service conductors "attached" to it to make it a mast.

The mast is nothing more than the upward raceway.

If you look up the definition of a service mast it will call the conduit rising up out ouf the meter base a "mast" at times even though no service conductors are attached to it.

If it does get attached to, then, it must follow the rules of strength and support.

JAP>
 

jap

Senior Member
Occupation
Electrician
In California, Southern California Edison only allows rigid steel or IMC conduit for risers when attaching service drops.

That's one example, and, rightfully so if they are attaching to it, but, go online and look at Midamericanenergy.com/electric-service-connection for instance.

It shows examples of service masts that are on the side of a house, and, not attached to.

In that case it the riser would not be required to support the strain of any conductors attached to them.

Oh well,,,, to each his own.

JAP>
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Yes, that's the a mast, but, it doesn't have to have service conductors "attached" to it to make it a mast.

The mast is nothing more than the upward raceway.

If you look up the definition of a service mast it will call the conduit rising up out ouf the meter base a "mast" at times even though no service conductors are attached to it.

If it does get attached to, then, it must follow the rules of strength and support.

JAP>


Where do you find the definition of a service mast in the nec.
 

kwired

Electron manager
Location
NE Nebraska
Yes, that's the a mast, but, it doesn't have to have service conductors "attached" to it to make it a mast.

The mast is nothing more than the upward raceway.

If you look up the definition of a service mast it will call the conduit rising up out ouf the meter base a "mast" at times even though no service conductors are attached to it.

If it does get attached to, then, it must follow the rules of strength and support.

JAP>
Where is this definition. I don't see anything in art 100 or 230 which is were I would expect to find it if there was one.

Note 230.28 that has been quoted a couple times here is titled "230.28 Service Masts as Supports."

I have on occasion installed or run into masts used as support for other than service applications as well though NEC seems to only focus on "service masts".
 