jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
That's not in the California Electric Code. CEC is same as NEC. That sounds like a local interpretation of 230.38.In Cali the last 10' of the service risor needs to be a continuous piece of Rigid, anything before that could be Emt.
SF has more stringent rules, in fact they only allow rigid. Although that rule makes it a moot point, most SF houses actually don't have masts going through the eave (most houses don't have eaves) or even as high as the roof anyway. There are still plenty of drops supported by insulators attached to houses, although PG&E will probably replace them given the opportunity.
PG&E probably wouldn't attach to vertical MT mast anywhere either. (Well, at least, a project manager wouldn't approve it. The lineman probably wouldn't care.) Now, horizontal service riser sections, supported by the eave or roof or wall... Not sure if there's a written down rule in the Greenbook. They seem to care more about the size of the lags you use to attach the riser, although it's not clear if they care how much wood you put those lags into. (Drive 3/8" lags into 1/4" plywood and you may meet the letter of their requirements.)
Not that I would push the boundaries. Rigid is standard practice here and anyone would look at you funny if you tried to argue otherwise.