It is my understanding after reading NEC Article 314-28(A)(3) that if I have conductors #4 and larger in a raceway and want to use an 'LB' that I have to comply with the markings inside the 'LB'. In other words if I do not violate the maximum quantity of conductors as marked on the inside of the 'LB', and do not have conductors larger then what is stamped on the inside of the 'LB' then I am in compliance with this code section.
Now if I have an 'LB' on a 3" raceway and have 4#250Kcmil & 1#2/0(G) and the raceway is marked, indicating that the maximum number of conductors allowed is three, and the maximum size conductor allowed is 400Kcmil. With this situation it is my understanding that I can not comply with this code section 314.28(a)(3).
Am I right? or what am I missing if I am wrong?
[ December 20, 2004, 03:46 PM: Message edited by: warrenwaldrop ]
Now if I have an 'LB' on a 3" raceway and have 4#250Kcmil & 1#2/0(G) and the raceway is marked, indicating that the maximum number of conductors allowed is three, and the maximum size conductor allowed is 400Kcmil. With this situation it is my understanding that I can not comply with this code section 314.28(a)(3).
Am I right? or what am I missing if I am wrong?