Re: The use of 'LB's
Dave,
I am just applying the code rule as it appears in 314.28(A)(3). If the conduit body is not listed for the number and size of conductors, then you must follow the requirements of 314.23(A)(1) and (A)(2). As this point the size and number of conductors is limited only by the raceway wire fill requirements.
Don
Dave,
I am just applying the code rule as it appears in 314.28(A)(3). If the conduit body is not listed for the number and size of conductors, then you must follow the requirements of 314.23(A)(1) and (A)(2). As this point the size and number of conductors is limited only by the raceway wire fill requirements.