Re: the use of two wire romex in three-way switch loop
Karl,
About pre-1999, I just checked my '93 NEC and I see no exceptions about "not needed" conductors of a circuit. Where did you get that from? It just says all conductors of a circuit including EGCs. ???
I don't have my 93 handy, but the wording in the 96 is as follows;
Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be contained within the same raceway,cable tray, trench, cable, or cord.
the wording of the 99 is as follows; (additional or changed wording in italics)
Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be contained within the same raceway,
auxiliary gutter, cable tray, trench, cable, or cord,
unless otherwise permitted in accordance with (1) through (4)
the wording of the 02 is as follows; (additional or changed wording in italics)
Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors
and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, trench, cable, or cord, unless otherwise permitted in accordance with (1) through (4).
This is the way I interpret these paragraphs.
Note: This is my opinion, which is no more than just that. (see the Handbook thread concerning opinions
)
The conductors of a given circuit can not be intalled in more than
one raceway, auxiliary gutter, cable tray, trench, cable, or cord, unless otherwise permitted in accordance with (1) through (4).
I don't see the wording requiring unecessary conductors in a raceway, auxiliary gutter, cable tray, trench, cable, or cord.
Now,
When using two-conductor travelers, part of the circuit will be missing the hot and part of it will miss neutral (currents
another common wiring method is a two wire switch drop, this does nullify the MF, but this is still missing atleast one or more conductors associated with a given circuit, and even if we add the grounded conductor, with out designing this conductor to return or pass through the switch box to another point of connection as a current carrying conductor, we haven't achieved anything except wasting resources.
Roger