the use of two wire romex in three-way switch loop

Status
Not open for further replies.

sparky902

Member
A Master electrician at work says that it isn't legal to use 12/2, or 14/2, for the travelers in a three way switch loop. Doesn't the NEC allow the use of the two wire romex as the travelers, if the white wire is reidentified?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: the use of two wire romex in three-way switch loop

Yes, this is legal. Ask him what article he would quote that would deem it illegal.

Roger
 

amp-dude

Member
Re: the use of two wire romex in three-way switch loop

sparky, roger--

You can't use 12-2 or 14-2 because you have to have a return conductor (neutral) that runs with the supply conductors. And you can't use the equipment grounding conductor (bare copper) as a current-carrying conductor.

Or roger, do you set your 3-way circuits up differently than I do?

Cliff
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: the use of two wire romex in three-way switch loop

cliff,
300.3(B)(3) permits the use of 2 wire NM in 3-way circuits.
Don
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: the use of two wire romex in three-way switch loop

Cliff, the EGC (bare copper) would remain just that.

I don't understand what you mean by,
you have to have a return conductor (neutral) that runs with the supply conductors.
this is not in the NEC as far as NM.

Remember, we are talking about travelers, or one hot wire, in a non inductive wiring method, and unless these single conductors are entering a metal box, this would eliminate 300.20 as covered in 300.3

Roger
 

russellroberts

Senior Member
Location
Georgia
Re: the use of two wire romex in three-way switch loop

Roger,I think he's talking about feeding the 3-way on one end,carrying the neutral through the 3 wire to the other end, and taking the switch leg up to the lite from there.

I think. :)

russell
 
A

a.wayne3@verizon.net

Guest
Re: the use of two wire romex in three-way switch loop

I used 2 wire travelers many times over the years,
In most cases a standard 3 way fed from one end and switched from the other,or a dead ended 3 way uses 3 wires.There are some cases in which it is not necessary to use the 3 wire nm.Where there are multiple switches on a circuit(multi gang) and the neutral from this circuit is already there
Then you can use a 2 wire traveler in lieu of the more expensive 3 wire.Or when there is a 3 way 4 way 3 way switching system and at the 4 way there is a single pole switch then I have run 2 2 wires one as a feed (hot /neutral) and one as travellers.I have seen guys run 2 wire travelers to another circuit and use that neutral :eek: IMHO
as long as you are carefull that you don`t share a neutral from another circuit there is nothing wrong with this
 

sparky902

Member
Re: the use of two wire romex in three-way switch loop

Thank-you gentlemen for answering my question so fast.

I did some more investigating on the subject myself, and found some information in Mike Holt's, "1999 NEC Illustrated Changes" book, page 14 figures 2-2 and 2-3. Figure 2-3 states:
"white conductors must be re-identified when used as travelers between 3 and 4-way switches".

Thank-you
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: the use of two wire romex in three-way switch loop

Don

Please explain 300.3(B)(3) to me. I do not see how this is allowed. How are you going to comply with 300.20?

I think that 300.3(B) prohibits 12-2 or 14-2. The grounded conductor is not in the same raceway.

What about EMF?

Mike P.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: the use of two wire romex in three-way switch loop

Mike,
Using NM cable there is no requirement that all of the conductors of the circuit be in the same raceway. 300.20 can be complied with by using NM connectors listed for more than one conductor or by using nonmetallic boxes. Yes, these installations will create more EMF, but that is not a code issue at this time.
Don
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: the use of two wire romex in three-way switch loop

Ron,
Read part (3) of the same section in the '99 and '02 codes. The answers given on this board are normally based on the 2002 code unless the original post specifies an earlier code.
Don
 

hurk27

Senior Member
Re: the use of two wire romex in three-way switch loop

You do not have to run a grounded conductor with a switch loop as per.
404.2
Exception: Switch loops shall not require a grounded conductor.
 

karl riley

Senior Member
Re: the use of two wire romex in three-way switch loop

Yes, the switch loop is different from the travelers.

But those who cite the change in 300-3(b) in 1999 as allowing the use of 2-wire travelers, you are correct as to Code unless one circuit supplies the hot and another circuit supplies the neutral. There may be no metallic enclosures until the circuits get back to the panel. Then, according to 300-20 you would have to cut a slot in the box between where the two circuits enter. Obviously not allowed, so that set-up would not work.

But if you use parts of only one circuit to feed the hot on one end and neutral on the other, you are satisfying the Code change, as long as no metal is traversed.

But do you think that the sometimes huge magnetic field that is set up in the whole area served by the three-way lights is something an electrician wants to set up? To save a couple of bucks? I can guarantee you that in office space this field would make the use of computers in the area probably impossible, due to the strain on the users' eyes due to the jitter. So why say it's OK, even though this Code change lets you get away with it?

Karl
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: the use of two wire romex in three-way switch loop

In the above question using the 2 wire for travelers:

You are required to combine all grounds in each three-way switch box.

This creates paralleled egc's.

Is this not a violation of 310.4?

Mike P.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: the use of two wire romex in three-way switch loop

After reading my post it does not make sense. I will leave it maybe someone can spin-off of it.

Mike P.
 

karl riley

Senior Member
Re: the use of two wire romex in three-way switch loop

Mike, I just checked: 310-4 refers to phase, neutral or grounded conductors, not to equipment grounding conductors.

Anyone have a comment on my previous post? I need feedback. I have no idea why 300-3(b) was changed in 1999. It was a thoroughly sound rule: keep all the conductors together. The NM exceptions take us back to knob and tube runs. What was the purpose of the change? Anyone know?
Karl R.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: the use of two wire romex in three-way switch loop

Hello Karl, I see and have thought about the EMF angle before in this wiring method, but in my case it has been residential and no more than a hall way light or two.

In the commercial aspect, I could see heavy loaded flourescent circuits causing a substantial increase in the problem.

With the NEC sell out to the metalic industry disallowing NM above suspended ceilings in commercial settings, I can also see this method being more of a convenience, and in turn, adding to the problem again.


Now, I must ask, where was this method prohibited before the 99 code cycle. The wording of 300.3 even in the 96 code, simply intended that all conductors of one circuit be in a common raceway or cable if all conductors were needed. If all were not needed, they were never required to be installed in a raceway or cable just to waste resources.

Roger

[ July 02, 2003, 09:53 PM: Message edited by: roger ]
 

karl riley

Senior Member
Re: the use of two wire romex in three-way switch loop

Roger, it's true that 300-3(b) has to be observed in metal conduits, so in the case of large loads large net currents will not be created if Code is observed.

About pre-1999, I just checked my '93 NEC and I see no exceptions about "not needed" conductors of a circuit. Where did you get that from? It just says all conductors of a circuit including EGCs. ???

When using two-conductor travelers, part of the circuit will be missing the hot and part of it will miss neutral (currents).

I am curious why NM was exempted in 1999, since all recent revisions have reduced EMF sources (eliminating currents on gas pipes, eliminating neutral on dryer cases and whatever they are touching, eliminating neutral on pipes supplying an outbuilding). These were all progressive steps in keeping magnetic field levels to insignificant.
Karl
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: the use of two wire romex in three-way switch loop

Karl,
About pre-1999, I just checked my '93 NEC and I see no exceptions about "not needed" conductors of a circuit. Where did you get that from? It just says all conductors of a circuit including EGCs. ???
I don't have my 93 handy, but the wording in the 96 is as follows;

Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be contained within the same raceway,cable tray, trench, cable, or cord.

the wording of the 99 is as follows; (additional or changed wording in italics)

Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be contained within the same raceway,auxiliary gutter, cable tray, trench, cable, or cord, unless otherwise permitted in accordance with (1) through (4)

the wording of the 02 is as follows; (additional or changed wording in italics)

Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, trench, cable, or cord, unless otherwise permitted in accordance with (1) through (4).


This is the way I interpret these paragraphs.

Note: This is my opinion, which is no more than just that. (see the Handbook thread concerning opinions ;) )

The conductors of a given circuit can not be intalled in more than one raceway, auxiliary gutter, cable tray, trench, cable, or cord, unless otherwise permitted in accordance with (1) through (4).

I don't see the wording requiring unecessary conductors in a raceway, auxiliary gutter, cable tray, trench, cable, or cord.

Now,
When using two-conductor travelers, part of the circuit will be missing the hot and part of it will miss neutral (currents
another common wiring method is a two wire switch drop, this does nullify the MF, but this is still missing atleast one or more conductors associated with a given circuit, and even if we add the grounded conductor, with out designing this conductor to return or pass through the switch box to another point of connection as a current carrying conductor, we haven't achieved anything except wasting resources.

Roger
 