Re: the use of two wire romex in three-way switch loop
Roger, there seem to be two threads being discussed here, but to get back to "not needed", I think I understand what you are saying. Correct me if I'm wrong.
You are saying you don't need a neutral in a switch leg. Right. This is part of the design of a three-way. Noone disagrees.
You are also saying you don't need a neutral (grounded conductor)to run with the travelers. I agree that you can wire this way (two wire)as long as you think it's OK to use a hot from one end (and cap the neutral) and use a neutral from the other end (and cap the hot).
No contemporary books on wiring show this as an accepted practice, but you can make a case that it is allowed by 1999 Code and after. I would agree, and that is what bothers me, since most electricians I know are not aware of the strength of the magnetic field caused by the net current loop set up by using two-wire travelers. (I am talking about more than a single light bulb).
The loop effect generates a high and even magnetic field within most of the loop. The travelers are one half of the loop. The psrt of the circuit which goes between the two switches is the other part of the loop, since this section contains either a hot carrying current or a neutral carrying current, but not both. So you have the loop effect.
The magnetic field strength needed to make a computer monitor jitter and to increase a child's chanced of leukemia (according to the World Health Organization - WHO)is about the same, starting at 5 milligauss. This can be generated by one amp of net current depending on distance to the conductors.
So my point is(sorry if I'm too far off Code discussion)that why do this to a building just to save the difference between two-wire and three-wire NM cable?
Karl