Eddy Current
The word "ground" has no meaning when discussing the rules of the NEC. Are we talking about the grounded conductor or are we talking about the Equipment Grounding Conductor?
EGC.
This does not make any sense?130208-2345 EST
A likely reason, and it might be good if the EGC was insulated, is:
Consider an EGC that is the same material of wire and the same diameter as the Hot wire. At the end of the run short Hot to EGC. The resulting voltage at the shorted point relative to the EGC bus at the main panel is about 1/2 of the Hot voltage.
If you have only a single EGC, then some of that 1/2 voltage appears at other points along the EGC.
In secondary circuits, a ground wire is a common term for the EGC. I doubt it would be confused with the grounded conductor except among those that wouldn't normally be allowed to post here anyway. YMMV.
Really? You think there is some chance the OP or the ones making the industrial standard or someone here is confusing a circuit's "ground wire" with the "grounded conductor"? Come on now.Agreed. The word "ground" also gets used for the GEC also.
Well a GEC would not not get pulled in alongside each circuit so could hardly be confused with the "ground wire" being discussed by the OP could it?Yes, but I see the word "ground" often used for GEC also and sometimes it is hard to tell what somebody is asking.
For example, not an untypical post/question:
I am installing a 400A service with two 200A panels. One panel will feed a 100A sub panel. What size ground do I need?
OK. Got it. Surrounding context sure helps to clarify the use of the term and without supporting info our loose use of the term "ground" does leave one having to guess.I was merely making a comment that the use of the term "ground" is often used for both a EGC and a GEC.
Like in my fictional example:
What "ground" would this person be referring to?
I doubt this since some of higher ups are actually on the board that wrote the NEC code book.
Maybe they should have determined why the fan casing became energized. Running a separate EGC with every circuit even though they are in same raceway may not have helped out with that incident at all, assuming code was met otherwise. Next they will want bonding jumpers for bonding jumpers to assure that bonding jumpers are effective.Ok i think im seeing why they might want this now but in a commercial building inside the plant why would they need this?
I was also thinking about tray cable that is used through out the plant and it does not have a ground per circuit, if it is say something like 12-3 tray cable there is only one ground in the cable.
Im not sure when the plant started making a ground per circuit required but it might have started when an employee was killed about 10 years ago from a fan casing becoming energized.
Hydraulic fans would do it.Maybe they should have determined why the fan casing became energized. Running a separate EGC with every circuit even though they are in same raceway may not have helped out with that incident at all, assuming code was met otherwise. Next they will want bonding jumpers for bonding jumpers to assure that bonding jumpers are effective.![]()
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.
Where circuit conductors are spliced within a box, or terminated on equipment within or supported by a box, any equipment grounding conductor(s) associated with those circuit conductors shall be connected within the box or to the box with devices suitable for the use in accordance with 250.148(A)through (E).
Exception: The equipment grounding conductor permitted in 250.146(D) shall not be required to be connected to the other equipment grounding conductors or to the box.