celtic said:...unless it's busted in the closed position...
I know... watch everyone go try and work on one tomorrow get belted...
celtic said:...unless it's busted in the closed position...
jeff43222 said:Thanks for all the help. I think a solution has been found!
I thought it did if you intended to use the thermostat as one of the required disconnecting means.iwire said:FYI the NEC does not require the thermostat to break both legs.
Never assume it does.
Have you read:iwire said:FYI the NEC does not require the thermostat to break both legs.
kbsparky said:I thought it did if you intended to use the thermostat as one of the required disconnecting means.
Yes, that was the basis of my response.celtic said:Have you read:
424.20(A) & (B)?
This is correct. Besides, even a T-stat that did operate both legs, would likely never break both legs at the same instant.stickboy1375 said:A 240v load won't operate on 120v, it's the same as a 120v load won't operate without a neutral... Even a 240v Tstat will only break 1 leg in operation, but when you move it to the OFF position, then it will break both legs for servicing....
LarryFine said:This is correct. Besides, even a T-stat that did operate both legs, would likely never break both legs at the same instant.
That's one reason 2-pole breakers have a common trip. Even two identical fuses in series will rarely both blow under overload or short conditions.
A 240v heater will operate at 1/4 power on 120v. There are 120v baseboards, but you have to go out of your way to find them.
Because when you halve the voltage across a given resistance, the current also halves. Since power is voltage times current, half of a half is one quarter (0.5 * 0.5 = 0.25).stickboy1375 said:How come it would be 1/4 power and not 1/2?