What code section is that?![]()
You know..... the "Keep-'em-honest" Code.
What code section is that?![]()
Bonding the sprinkler may be a violation of the fire code.
This local one.What code section is that?![]()
Bold is in the code....250.64(B). Revise this section as follows:
250.64(B) Securing and Protection Against Physical Damage. Where exposed, a grounding electrode conductor or its enclosure shall be securely fastened to the surface on which it is carried. A 4 AWG or larger copper or aluminum grounding electrode conductor shall be protected where exposed to physical damage. A 6 AWG grounding electrode conductor that is free from exposure to physical damage shall be permitted to be run along the surface of the building construction without metal covering or protection where it is securely fastened to the construction; otherwise, it shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor. Grounding electrode conductors smaller than 6 AWG shall be in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, electrical metallic tubing, or cable armor. Exposed grounding electrode conductors or cable armor shall not be installed on the outside of a building or structure. 6 AWG or smaller grounding electrode conductors shall not be installed exposed below 5'.
Sprinkler must be bonded. "Metal water pipeing system" It doesent matter what the water is being used for.
I was joking about the junkie theft. :smile:e57 said:This local one.
If you don't bond it to the water system you will have a difference of potential between the pieces of steel to which the person connecting them gets shocked.
Heres question for you guys,
Do you Or should you bond from your water pipes to cast iron sewer pipes in basement?
Don't know whether you should but I have never seen anyone bond a cast iron sewer pipe. It is not likely to become energized therefore I see no reason to do it.........
Yes - out of town guys find this one out the hard way when they get nailed by an inspector who feels that it should be that way everywhere. They ask - "Are you joking?" Which sets up a bad tone for the rest of the inspection....I was joking about the junkie theft. :smile:
However I see you were serious- thought you were joking.
Curiousity would have made me amp-clamp the wire.It (2.3 volts) went away because I made the potential difference zero.