The utilities wires (triplex) come to the weather head a then splice on to usually copper that the electrician usually runs. Can that wire be THHN?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Those conductors would also require a wet location rating. THHN is only for dry locations and damp locations.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
THWN/THHN is not guaranteed to be sunlight resistant. If it is, it will be part of the labeling on the cable. So check the insulation labeling to verify sunlight resistant. All I've seen recently have that rating.
 

Volta

Senior Member
Location
Columbus, Ohio
I agree with Mark that generally the dual or tri-rated (with MTW) often say sunlight-resistant or similar.

Whether they actually hold up to years in the sun may still be debatable though...
 

jusme123

Senior Member
Location
NY
Occupation
JW
I agree with Mark that generally the dual or tri-rated (with MTW) often say sunlight-resistant or similar.

Whether they actually hold up to years in the sun may still be debatable though...

any cable or wire exposed to the elements will eventually fail, even SE cable- it dries out and cracks
 