THHN/THWN WIRE

Status
Not open for further replies.

Browndogg

New User
Location
Dallas Texas
Occupation
Electrician
I'm working on a remodel and the grounding to the service (s) is laking. I'm working up a price to bring the grounding up to code. So to keep the cost down would like to run the grounding conductor free air.

Question: Is thhn/thwn wire plenum rated?
 
Thats a code violation, unless all circuit conductors are in the same raceway, the impedance will be too high and a ground fault won't clear....the magnetic fields do not cancel.
 