Hendrix
- New England
Table c.1 Tells me that I can pull 4 350kcmil conductors through a 2.5 in. piece of emt. Can a one ought grounding conductor be included in that run ?
Is it because it's a non current carrying conducor or is it dependant upon the total circular mills of the five cables in relation to the size of the emt ?Yes. Personally, I'd upsize it to 3" though.
Jason
What do you say, Lakee ?In Chapter 9 it says you can pull 4-350's through a 2 1/2 " EMT and that is what you can pull so if you want to include a 1/0 you would have to increase the conduit size. So my answer would be "no" to what you asked. That is assuming you mean you are pulling the 4-350's and want to include a 1/0.
Thank you, RogerWireguy, look at Table 5 in chapter 9, 350 kcmil has an area of 0.5242 sq" and 1/0 has an area of 0.1855 sq " which equates to total area of 2.2823 sq" and Table 4 gives 2.5" EMT @ 40% an area of 2.343, so (4) 350 kcmil's and (1) 1/0 will be fine.
Roger
Actually the wire fill tables are in Annex C and not in Chapter 9. The information in Annex C is not part of the code.In Chapter 9 it says you can pull 4-350's through a 2 1/2 " EMT and that is what you can pull so if you want to include a 1/0 you would have to increase the conduit size. So my answer would be "no" to what you asked. That is assuming you mean you are pulling the 4-350's and want to include a 1/0.
No problem, we are all here to learnThanks, I ment to put Anexx C just was looking at chapter 9 on my index. Hmm never knew that the anexxs were not part of the code, so what is the purpose of them?
Hendrix, sorry gave you wrong info....and thanks for the corrections
Roger
From 90.3cccccThanks, I ment to put Anexx C just was looking at chapter 9 on my index. Hmm never knew that the anexxs were not part of the code, so what is the purpose of them?
...Annexes are not part of the requirements of this Code but are included for informational purposes only.