Had a job Tuesday evening, building flooded and busway was in the path of the water, no dams around the busway chases between floors. I informed the customer if I meggered the busway and the readings were unacceptable I would not re-energize the busway. This system had been on line 30 hours since the flood and at no point had been de-energized.
Powered down the busways 2000 amp and 1600 amp.
Meggered at 1000 VDC, A Phase-163,000 OHMS and it was the same for all phases to ground and phase to phase, both busways. triple checked all busway switches were off and looked for any busway taps, all was off. I explained to the customer and told them I would not re-energize as previously explained and told him I could not recommended he re-energize. Long and short a temporary was installed, bypassed the wet/defective portions. The portions of the busway removed had water pouring out of them. The portions left intact meggered in excess of 2 gigohms.
Now this busway was up and running with no issues other that a possibility of blowing up at any point.
Had a 45 kva transformer (another site) under sewage and other that the steam it had output voltage and the customer was using this to operate pumps.
Had a busway that had been tripped off due to a UV operation and was reset, at one point we were hired to megger it readings were in the 1-2 megohm range. Busway was shut down and a 90 was located with an accumulation of rust, filings dirt muck and evidence of past water intrusion.
Has anyone else been involved with distribution equipment that should obviously have been damaged and should have operated protective devices but didn't?
Any thoughts on why?
Powered down the busways 2000 amp and 1600 amp.
Meggered at 1000 VDC, A Phase-163,000 OHMS and it was the same for all phases to ground and phase to phase, both busways. triple checked all busway switches were off and looked for any busway taps, all was off. I explained to the customer and told them I would not re-energize as previously explained and told him I could not recommended he re-energize. Long and short a temporary was installed, bypassed the wet/defective portions. The portions of the busway removed had water pouring out of them. The portions left intact meggered in excess of 2 gigohms.
Now this busway was up and running with no issues other that a possibility of blowing up at any point.
Had a 45 kva transformer (another site) under sewage and other that the steam it had output voltage and the customer was using this to operate pumps.
Had a busway that had been tripped off due to a UV operation and was reset, at one point we were hired to megger it readings were in the 1-2 megohm range. Busway was shut down and a 90 was located with an accumulation of rust, filings dirt muck and evidence of past water intrusion.
Has anyone else been involved with distribution equipment that should obviously have been damaged and should have operated protective devices but didn't?
Any thoughts on why?