Phillip Land
Member
- Location
- Rome, Ga, US
I thought the entire point of moving the main breaker from the inside panel to the outside was safety.Your service disconnect is outside in the meter main. The panel inside is a subpanel and requires ser which is 4 wires. You need a neutral, 2 hots and an equipment grounding conductor. No bonding in the second panel-- everything is done outside at the meter main
1. the means of disconnecting all power from a building in an emergency (such as a fire) can be reached more quickly
2. With a main breaker outside, there is now overcurrent protection and short circuit protection on the conductors passing through the structure of the building where there wasn't before
With that being said, I understood that the "em disco" was a way to add a disconnecting means to a structure like a detached garage or a pool house if the main breaker (Service disconnecting means) happened to be on the main house next to its main breaker.
Here in metro-Atlanta, it's pretty common to find the service equipment mounted on the main house next to the meter, then a "4 - wire feeder" (usually underground) to the secondary structure and in through an LB and over to wherever the load center is.
Again, maybe I'm misunderstanding, but I thought that the new 2020 code was in part to help emergency personnel ensure that power was shut off to the building in question.
I think the new rules will continue to allow service equipment to be installed in the main panel as long as the meter and newly required em disco are installed on the other side of the wall or the service conductors are outside the building (ie under 2" concrete)
I always thought that seeing a row of meters on the outside of a 5 or 6 unit condo seemed to be inherently stupid. If there's a structure fire, it seems smarter to be able to be outside the building and shut everything off from there than have to go inside each unit and turn off power at the panel
sorry for being so long winded