1793
Senior Member
- Location
- Louisville, Kentucky
- Occupation
- Inspector
Situation:
Kitchen >> fluorescent fixture over Island wired from the end of the fixture. 14/2 romex stripped about 20" for connection in the fluorescent.
Customer >> removed fluorescent and wants to install a chandelier over the Island.
Problem >> There was no box for the original install. The 14/2 romex is long enough to reach to a box to be installed about 15" away.
Question >> Since the 14/2 has been stripped; What would you do.
I have thought about cutting some 14/2 and sliding the outer jacket off and sleeving the existing 14/2 to the box I will add.
This is a two story with finished room above the Kitchen.
Kitchen >> fluorescent fixture over Island wired from the end of the fixture. 14/2 romex stripped about 20" for connection in the fluorescent.
Customer >> removed fluorescent and wants to install a chandelier over the Island.
Problem >> There was no box for the original install. The 14/2 romex is long enough to reach to a box to be installed about 15" away.
Question >> Since the 14/2 has been stripped; What would you do.
I have thought about cutting some 14/2 and sliding the outer jacket off and sleeving the existing 14/2 to the box I will add.
This is a two story with finished room above the Kitchen.