iwire said:
Al with both switches 'down' you have a 310.4 issue IMO
I know this has been hashed thru on the Forum before. I agree that it is not a safety issue, with respect to inductive heating when a nonmetallic method is used (EMF is another matter, but that's not in the Code yet).
The conditions (a), (b) and (c) to
Exception No. 1 under 310.4(A) are all met by the circuit in my sketch above. The technical Code issue is in the shopping list of installations of small gage paralleled conductors given in the first paragraph of
Exception No. 1. "Control power" is hard to stretch to fit my sketch.
However, I submit, the Code issue is the imprecise meaning of "parallel" in the context of 310.4.
My sketch illustrates a hot conductor paralleled with the common-common conductor, in one of four switch states, but the paralleling is not for voltage drop improvement or reduction of conductor size. So, I would say, 310.4 doesn't apply.
If the meaning of "parallel" in 310.4 were a blanket meaning covering all possible parallel installations, then installing metal raceway between a meter socket and the service disconnect would be a violation.