Gar, thanks for doing the test. Interesting. I had done a similar test, although with an unloaded 1/4 horse 3 phase 208v motor. I started out with motor running at full voltage. As I decreased the voltage, the current went down and down all the way to 30v, where it started to rise. At that point, the motor was barely turning.
I didn't post the info because an unloaded motor acts way different than a loaded motor. Your test looks good.