sfork2020
- Quogue N Y
- Electrician
I am rewiring a Kaeser Compressor The model number is an a S 25 the unit was wired by somebody else not done correctly. Is asking for number 2 AWG WIRE . consumption in amps total 75 then it says pre-fuse amp 110 Amps end it must be dual element time delay fuses. I believe the fuses should be larger I calculated from table 430-52 percentage of full load current75X175= 131.25 next available size would be 150 . any exceptions for 439-52 says dual element fuse shall be permitted to be increased but not more than 225% of the full load motor .Making sure this is correct what I have to use a larger disconnect for those fuses?