Re: Three phase load preference
I guess I should restate what I added to my other post as after thinking about it in the several times I was called out for this problem it was only in three cases that there was a loss of the MGN that caused primary return current through the service grounding that turned out to be the cause. So I guess it wouldn't a main reason.
The other case it was a loss neutral at the transformer. another was a break in the underground neutral on the secondary side after the transformer, and one was even voltage drop in the neutral between the service and the transformer 800' run the POCO ran a triplex 250,250,250,2/0 AL. and the 200 amp service was very unbalanced as well as very over loaded. The meter was tapped to feed the barns as well as the house, and all was using the neutral as the grounding conductor.
We did have one that had the MGN snapped by a falling tree down the road about a ? mile. I guess it went unnoticed until the grounding to Earth got weak and the voltage started to rise. the home owner remembered that that tree fell about 3 months before this, from a storm but didn't knock out the power.
But I don't see where current can pass through a transformer as current can only return to source. unless it is caused by another service down the road fed from the same transformer bank or from the primary side? why would an open 4-wire delta cause voltage to Earth on the neutral on the secondary side of the transformer that a 120/208 Y wouldn't? as the current should return back to source (generator plant) and not be drawing current from Earth?
And what about all those old 240 volt motors that don't like 208? The farmer would have to change them or add boost transformers.
I guess I should restate what I added to my other post as after thinking about it in the several times I was called out for this problem it was only in three cases that there was a loss of the MGN that caused primary return current through the service grounding that turned out to be the cause. So I guess it wouldn't a main reason.
The other case it was a loss neutral at the transformer. another was a break in the underground neutral on the secondary side after the transformer, and one was even voltage drop in the neutral between the service and the transformer 800' run the POCO ran a triplex 250,250,250,2/0 AL. and the 200 amp service was very unbalanced as well as very over loaded. The meter was tapped to feed the barns as well as the house, and all was using the neutral as the grounding conductor.
We did have one that had the MGN snapped by a falling tree down the road about a ? mile. I guess it went unnoticed until the grounding to Earth got weak and the voltage started to rise. the home owner remembered that that tree fell about 3 months before this, from a storm but didn't knock out the power.
But I don't see where current can pass through a transformer as current can only return to source. unless it is caused by another service down the road fed from the same transformer bank or from the primary side? why would an open 4-wire delta cause voltage to Earth on the neutral on the secondary side of the transformer that a 120/208 Y wouldn't? as the current should return back to source (generator plant) and not be drawing current from Earth?
And what about all those old 240 volt motors that don't like 208? The farmer would have to change them or add boost transformers.