I have balanced three phase load. I do not need to bring neutral i.e grounded conductor however code requires grounded conductor brought to the service disco. So what size should the grounded conductors be? What table should be used?
Sent from my SM-G935U using Tapatalk
That was my point. So neutral wouldn't be the path for motor fault current.You wouldn't. None of these posts have suggested that you would.
In my experience, 3-phase motors are usually one of the best balanced loads.Don't confuse a balanced 3 phase load with a load that is a 3 phase motor.
JAP>
That was my point. So neutral wouldn't be the path for motor fault current.
For us at least, a ground (earth) fault would go back, via the earth conductor, to the supply transformer.
Neutral does not play a part.
In my experience, 3-phase motors are usually one of the best balanced loads.
Most our LV supplies are wye systems.For us, the path for a ground fault between the supply transformer and the service disconnecting means is the grounded circuit conductor.
For a wye system, the grounded circuit conductor is the neutral.
Overcurrent protection.What clears your fault in a ground fault scenario if the neutral at the service disconnect doesn't play a role then?
JAP?
Most our LV supplies are wye systems.
Yes, it is usually the case here that the neutral is grounded at the supply transformer.
But the common 3-phase motor doesn't have a neutral so it plays no part in a ground fault.
The ground (earth) conductor which is a mandatory requirement does.
Neutral and ground are two different things. Neutral is not connected to a three phase motor. Ground is.And here, in this case, the ground (earth) conductor between the transformer and service disconnecting means is the neutral. So it does play a part in a ground fault.
I'm not sure what is difficult to understand about that.
Neutral and ground are two different things. Neutral is not connected to a three phase motor. Ground is.
Neutral and ground are two different things. Neutral is not connected to a three phase motor. Ground is.
There are major differences between our systems any yours. We don't have a "ground (earth)" conductor on the line side of the service disconnect. For a grounded system, we have a neutral that functions as a circuit conductor for line to neutral loads and also functions as the fault return path back to the utility transformer. On the load side of the service disconnect, those two functions use two separate conductors. A neutral for the actual line to neutral load current and a grounding conductor for fault clearing. In the event of a "ground fault" at the motor in the system being discussed here, the fault return path would be via to Equipment Grounding Conductor, to the main bonding jumper (the point in the service equipment where the neutral and grounding conductors are connected together), to the neutral back to the supplying transformer.Neutral and ground are two different things. Neutral is not connected to a three phase motor. Ground is.
Overcurrent protection.
There is a solid conductor path back to the transformer point.star point.The Overcurrent protection device will trip on a phase to phase fault or overload between the phases only, sure, but , it will not trip on a phase to case or (Otherwise known as a Ground Fault) unless there is a path for the current to return to the source (which is the XO terminal at the Utility Transformer) quickly.
JAP>
There is a solid conductor path back to the transformer point.star point.
There is a solid conductor path back to the transformer point.star point.
Ground and neutral are not the same thing.
Sure, the neutral may be grounded but why would you neutral rather than ground at the motor?
There is a solid conductor path back to the transformer point.star point.