lazorko
Member
- Location
- Philadelphia
The local "Y" recently had its 3 phase pool pump motor replaced. For the past week, the motor has been running hot, noisy, and blowing fuses.
Cleaning and tightening loose connections and nicked conductors, I got the motor running again, though I thought it was running hotter than it should have. After two hours, "Y" called to say that the a fuse blew again.
The 5HP 3phase replacement motor nameplate indicates a voltage of 200V - but the facility is served by a delta connected 3phase. - the available voltage is 240V. Could this be the source of the problem?
Your help is appreciated by a cash-strapped non profit.