A | B | C | |
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
5 | 5 | ||
Total kVA | 50 | 45 | 45 |
Volts | 120 | 120 | 120 |
Amps | 416.67 | 375.00 | 375.00 |
Isn't this the same as sizing for the highest phase amps as calculated using the VA method?IMO the only way to determine breaker/panel sizing is to take the largest phase VA, multiply by 3, then solve for current using the balanced formula, this will guarantee the service/breaker/panel can handle the total load without overloading an individual phase, plus you will have some spare capacity.
Isn't this the same as sizing for the highest phase amps as calculated using the VA method?
In the example, the largest phase VA is 5000. 5000?3/208/sqrt(3) = 41.64 A. This would be the same as Phase A amps if we used 208/sqrt(3) = 120.0888 instead of 120 V.
I don't know if I am on the right track. But I would do this similar to the range calculations in 220.55 and the example in annex D(5)(a).
A- B 5
B- C 5
C- A 5 take twice the max connected between any two phases = 2 x 5 = 10 x 10,000 =
100,000/208 = 481 amps between two phases. 481/ 2 = 240.5 amps per phase 240.5 x 3 = 721.5 for the whole system.
I don't know if I am on the right track. But I would do this similar to the range calculations in 220.55 and the example in annex D(5)(a).
A- B 5
B- C 5
C- A 5 take twice the max connected between any two phases = 2 x 5 = 10 x 10,000 =
100,000/208 = 481 amps between two phases. 481/ 2 = 240.5 amps per phase 240.5 x 3 = 721.5 for the whole system.
I screwed up and used 5000 VA instead of the total Phase A 50000 VA. I should have gotten 416.4 A not 41.64.:ashamed1:Not quite following your thinking with the calc. Keep in mind that the 5000VA for the load divided by 120V is not the correct load current. the load current is 10,000VA/208V = 48A. (cos(30) difference)
In your load schedule, which I agree with, you got 50KVA, 45KVA and 45KVA for Phase A, B, and C respectively. If you add those together the value is 140KVA. Taking 140KVA/208/sqrt3 = 388A, by going to the next breaker up you are at 400A. That however is not going to be large enough since you have Phase A at over 400A.
By using the 50KVA*3 = 150KVA, then 150KVA/208/sqrt 3 = 416A (no surprise). So, yes you can use the largest phase amps, it would be the same thing. I like to stay in KVA as much as possible, especially if there is a transformer involved because there are standard transformer sizes that would be the driving factor in size selection, and they are all rated in KVA.
I screwed up and used 5000 VA instead of the total Phase A 50000 VA. I should have gotten 416.4 A not 41.64.:ashamed1:
After reevaluating my first calculation i realize it is wrong. But I would still do it according to 220.55 but not apply any demand factors while trying to keep the system as balance as possible.
Max single phase loads connected between any 2 phases is 5 x 2 x 10,000 = 100,000/2 = 50,000 per phase 50,000 x 3 = 150,000 / 208 x 1.732 = 417 amps per phase 50,000/120 = 417 amps per phase.
I know there are easier methods of coming up with the same answer. But I would stick with this one because this is how it shows in in the examples for range calculations. It is really no different other than not applying demand factors.