NEC 250 Question
NEC 250 Question
I know this tread is getting long. Earlier I noted that we discovered that some feeder panels did not have the same number of hots as neutrals. The EC hired by the GC has basically confirmed our one hour investigation and in deed the site does NOT meet spec. The EE designed it with no shared neutrals and that did not happen. I also learned that they found 12 branch circuits that they can not identify where they lead to. I am assuming they flipped breakers and nothing went off, but did not tone out where they lead. Plan is not to meet spec as they feel it meets code. Customer was short changed IMO.
Also, as I mentioned this is three separate buildings and classified as residential for building code even though it is a three phase wye service. The service enters building two, because it is in the center, but one and three are feed from 400amp disconnects in building two (after the 1600amp main panel). Buildings one and three also have around five sub panels with 42 breakers average. There are no ground rods or grounding system in building one or three and they get earth ground from building two only*. This was built in 2010/2011 and NEC code 2008 was the city's standard. There is one bond at the service panel, but as I read NEC 250.32 buildings one and three should have ground rods themselves. Remember, these are wood frame structures and no metal water pipes, building steel or ufer was available so that is why I say rods.
*If what I am told is correct, would buildings one and three not having their own grounding system be a code violation? It appears they are grounded, but in another building.
I know here in the Midwest, I would not want a lightning strike to have to go any further than necessary to find home. Through one building then underground and through a second building and out the side wall to the bonded ground rods seems dangerous.
250.32. Grounding Separate Buildings and Structures
(A) Grounding - To the Earth. Metal parts of the electrical system in separate buildings or structures supplied by a feeder, building or structure must be grounded to the earth to prevent the destruction of electrical components from superimposed voltage from line surges, unintentional contact with higher voltage lines, and voltage transients and to help prevent the build-up of static charges on equipment and material [250.4(A)(2).
Exception. A grounding electrode at a separate building or structure is not required where only one branch circuit (with an equipment bonding conductor) supplies the building or structure. Slide 209
DANGER - Failure to ground the metal parts of the electrical system to the earth can result in electric shock, fires and the destruction of expensive electronic equipment from lightning or high voltage line surges.
(B) Grounding - Effective Fault Current Path. To protect against electric shock from a ground-fault (line-to-case fault), dangerous voltage on metal parts of the electrical system must be removed in less than 1 second by opening the circuit overcurrent protection device. To accomplish this, the impedance of the fault current path must allow the ground-fault (line-to-case fault) current to raise to a value of at least 5 times and preferably 10 times the rating of the overcurrent protection device.
In order for the circuit overcurrent device to open and prevent dangerous voltage from remaining on metal parts of electrical equipment, noncurrent-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment must be bonded together and to the grounded (neutral) terminal at the electrical supply source in a manner that establishes an effective ground-fault current path.
(1) Equipment Grounding Conductor. An equipment grounding conductor [250.118], sized in accordance with 250.122, shall be installed with the feeder conductors to the separate building or structure to bonding equipment, structures, or frames .
Author?s Comment: The feeder equipment grounding conductor provided the low impedance path for fault current to ultimately return to the electrical supply source as required by 250.2(A)(3).
CAUTION: To prevent dangerous neutral current from flowing on the metal parts of the electrical system, in violation of 250.6(A), the grounded (neutral) conductor at the separate building or structure must not be bonded to either the equipment grounding conductor or to the grounding electrode system.
(2) Grounded (neutral) Conductor. Where (1) an equipment grounding conductor is not run with the supply to the building or structure, and (2) there are no continuous metallic paths bonded to the grounding system in both buildings or structures involved, and (3) ground-fault protection of equipment has not been installed on the common ac service, the grounded (neutral) conductor run with the supply to the building or structure shall be connected to the building or structure disconnecting means and to the grounding electrode(s). The size of the grounded conductor shall not be smaller than the larger of:
(1) That required by 220.22 (maximum unbalanced neutral load), or
(2) That required by 250.122 (equipment grounding conductor size).