Sleken

Member
Location
Oklahoma
Hello all. I have a customer that wants to install some mini-split air conditioners. Apparently, they can only be purchased in single phase 208-240 volt configurations. I need 62 amps on the secondary.

The customer has three phase 277/480 available with a 30 amp fusible bucket currently spared in the switchboard.

Hubbell-Acme Electric (Is Hubbell buying everything?!) says this isn't possible without a custom transformer.

This doesn't seem correct to me, but my experience is only with stepping down three phase to another three phase voltage.

Does anyone have any thoughts?

--Josh
 
Step down to 208Y/120 with a standard transformer and then balance the mini-splits across the three available L-L 208V circuits. The mini-splits should not care that the 208 is 2 out of 3 derived from three phase.

Sent from my XT1585 using Tapatalk
 
How are you calculating the 62A? If you are arithmetically summing the MCA's of several 1Ø units, that will not be correct for several units balanced on a three phase source.
 