Anybody have a clever idea on how to balance a three-phase generator output to a single-phase load using transformer(s)? The generator output is 30 kw three phase, and the single-phase load is 15 kw. The load is currently supplied by a utility voltage (single phase only) of 115/230V. The output of the three phase generator can be 120/208, 127/220, or 139/240. There are both 120 and 230V single phase loads. Goal of exercise is to use generator as backup w/ transfer switch. Would like to keep the backup voltage as close to utility voltage as possible.
Thanks
 

bennie

Esteemed Member
Re: Three Phase to Single Phase

You will need a 3 phase motor driving a 15 KW single phase generator. Best to get a single phase generator to start with.
 

santoro

Member
Location
Alaska
Re: Three Phase to Single Phase

No can do, need three phase to start Fire Pump Motor. Have generator and motor. Need to reasonably balance remanding single-phase load (shed when FP is called for). Looking for economical solution. May not be possible but still holding out for ingenious solution.
 

bennie

Esteemed Member
Re: Three Phase to Single Phase

santoro: Good luck! There is a lot I don't know, I will be interested if someone can resolve your problem.
 

bennie

Esteemed Member
Re: Three Phase to Single Phase

I have been thinking...Get 3 single phase panels, convert them for 120 volts only. Connect one phase to each panel. I would have to draw out a transfer switch setup. It may be 49 poles before finished :(

Connect the load circuits according to time and duration of each load.

[ June 23, 2003, 08:10 PM: Message edited by: bennie ]
 

bennie

Esteemed Member
Re: Three Phase to Single Phase

Sorry: I was changing my mind while you were answering. Yes it is important to balance the load on the generator as close as possible.
 

bennie

Esteemed Member
Re: Three Phase to Single Phase

I didn't think of that hook up. It appears to be an open delta to an open wye. With proper transformers it should work.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Re: Three Phase to Single Phase

Be careful with the Square D "Hoppy Hookup".

The single phase side is balanced, however the common three phase (think B phase) conductor current is 3x the other phases (think A and C). Your generator will definitly not be balanced.

Also the single phase line to line voltage will be 208V not 240.
 

engy

Senior Member
Location
Minnesota
Re: Three Phase to Single Phase

What am I missing here with the hoppy hookup?
(neutral current same as original 1-ph service?)
(primary common current 3x of other two lines?)

How is this hookup different from normal delta-wye?
(Besides only using 2 of 3 phases)

I assume the "existing" service was 120/240.

What am I not assuming? :confused:

[ July 14, 2003, 04:31 PM: Message edited by: engy ]
 

brian john

Senior Member
Location
Leesburg, VA
Re: Three Phase to Single Phase

If you want to get really inventative, and possible void the warranty. If this is a 12 wire generator design a contactor system that would connect the generaor single phase under "normal" operatoin. and three phase under "fire pump" ooperation. It is do-able.
 