hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
480V 50kVA 3 phase transformer nominal current is 60A.
208V nominal current is 139A.
100A primary OCPD is 166% and is acceptable if secondary OCPD is 125%.
Secondary OCPD would need to be 175A to be kosher.
Jon
Secondary only two legs are loaded third not loaded. Thats single phase not three phase. How can one calculate three phase fla secondary given above situation?
Sent from my iPhone using Tapatalk