Thank you for the many suggestions. I have revisited the customer site with the suggestions in mind, and have visited with the customer.
Here is an updated 'as is:'
View attachment 9460
One big correction is that the inside garage panel is a 200 A service entrance load center, not a 400 A. Thus, the 2/0 svc feed is now the correct AWG.
In the document shown it lists 6 violations:
1. No disconnect noting outside svc main & inside svc main (grouping)
2. Ground conductors exist from meter socket to svc entrance load centers
3. No GEC present for outside 200 A svc entrance load center
4. Ground-to-neutral bonding exists in what?s used as sub-panel (inside upstairs 100 A load center)
5. 14 tandem breakers exist in upstairs 100 A load center. Model BR3030BC100 allows for zero.
6. Not enough space between A/C units and outside panels
I will be installing an energy monitoring & logging system into this residence, and, a dedicated automated processor for all home functions including advanced lighting control. As a result of the audit, I will ask the customer to at minimum fix the violations related to surge and noise, specifically 2, 3 and 4. The actions I have asked for include:
2. Remove ground conductor from meter socket to 200 A outside svc entrance load center and from meter socket to 200 A inside garage svc entrance load center.
3. Install grounding rod just below outside 200 A svc entrance load center and add GEC to neutral bus.
4. Remove all ground-to-neutral bonding in inside upstairs 100 A load center (neutral & ground circuit wires are already 'pure')
Later this evening I'll have some more time to illustrate with existing images.
Many thanks for comments! I'm a lot more appreciative of the complexities of this particular site thanks to the assistance here.
Best regards,
Bill