Tighten tug and re-tighten ?

Status
Not open for further replies.

Natfuelbilll

Senior Member
Question 1...........
Who, when terminating a conductor, will tighten - then tug (or wiggle) - then re-tighten?

Question 2.........
Have you ever used a torque wrench to measure your efforts?
 

Mr. Wizard

Senior Member
Location
Texas
Question 1...........
Who, when terminating a conductor, will tighten - then tug (or wiggle) - then re-tighten?

Question 2.........
Have you ever used a torque wrench to measure your efforts?

Manufacturing plant here in town requires all lugs to be torqued, and they'll go behind you to verify. I don't mind doing it at other places, either. If the manufacturer has a specific value to tighten their lugs, may as well make it right.
 

quogueelectric

Senior Member
Location
new york
#1 Yes
#2 yes but usually only on critical loads /lugs such as Primary and or large current bussbar assembly. Rarely have I torqued a small Lower voltage conductor. Only when it is in the spec.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Question 1...........
Who, when terminating a conductor, will tighten - then tug (or wiggle) - then re-tighten?

Question 2.........
Have you ever used a torque wrench to measure your efforts?

1. We do. Especially since our inspector checks connections by wiggling the wires to see if they'll pull out. It's happened more than once....

2. No.
 

cadpoint

Senior Member
Location
Durham, NC
Question 1...........
Who, when terminating a conductor, will tighten - then tug (or wiggle) - then re-tighten?

Are you talking about the lug spinning as you tighten it, yes it happens?
Usually I'll get someone to hold the lug with a channel lock! If it's a case of you think you might have stripped the threads, you probably heard the squeal of the metal threads first and you are beyond the Limit of the Torque. (see link below)

Question 2.........
Have you ever used a torque wrench to measure your efforts?
Yes!

The first is a manufactures sight that sells torque equipment, while it might be above casual reading, there is a great diagram at the bottom of the page, Here !

This link Here gives and over view of U.S. Bolt torque specifications and what bolts to use when and where. Remember this is just the bolt not the nut :roll:

A nut specification is Here, another manufactures sight, note that the nut is closer to torque values you'll read about on any hardware/equipment that require and state torque limits, and why one should use a torque wrench, (OK, JUST MY OP!)

I'm a big fan of using a torque wrench!

Hope that helps!
 
Last edited:

Red Wiggler

Senior Member
Torque always

Torque always

We have a Standardize Acceptance Procedure (SAP) that we use on all of our jobs. We use calibrated torque wrenches on all of our bolts (minimum Grade 5, usually Grade 8 hardware) and torque screwdrivers when terminating on breakers. All nuts and screw heads are painted (with a stripe) to verify visually that they have been torqued. Everything is documented.
 

cadpoint

Senior Member
Location
Durham, NC
This is a link to a lug manufacture that shows their products and torque valves and some other appliable nut and bolt configurations and there legends and valves. Active viewers have seen this link before.

Thanks to a friend! :smile: :wink: :cool:
 

JES2727

Senior Member
Location
NJ
Question 1...........
Who, when terminating a conductor, will tighten - then tug (or wiggle) - then re-tighten?

Question 2.........
Have you ever used a torque wrench to measure your efforts?

I always torque larger conductors ( 1/0 and larger), but never smaller ones. I usually don't wiggle or tug or shake the wires, although I had a guy in my employ for a while who would tighten the lugs as tight as he could make them, then grab the wire with both hands and shake the heck out of it! Then he'd tighten it some more. That's the way he was taught and as far as he was concerned that was the only way to do it. I asked him to stop doing it that way and handed him a torque wrench. He didn't like it, but he did it my way.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Where in the gear torque specs or in the torque wrench instructions does it say:

'Torque, shake, repeat?':-?
 

ohm

Senior Member
Location
Birmingham, AL
We have a Standardize Acceptance Procedure (SAP) that we use on all of our jobs. We use calibrated torque wrenches on all of our bolts (minimum Grade 5, usually Grade 8 hardware) and torque screwdrivers when terminating on breakers. All nuts and screw heads are painted (with a stripe) to verify visually that they have been torqued. Everything is documented.

Sounds very professional. I noticed in your profile you're a Pre-Planner...whats that?
 

Red Wiggler

Senior Member
Pre-Planner

Pre-Planner

Sounds very professional. I noticed in your profile you're a Pre-Planner...whats that?


A Pre-planner is a person (usually comes from the field, Foreman, General Foreman, Super.) that takes a job that is under contract, or has a letter of intent and using AutoCAD lays out the service, underground, slabs, walls, overhead, cabletray, conduit racks, lighting (lighting controllers) special systems, fire alarm, creates panels schedules based on the pre-plan, temporary layout, etc. Anything that is needed to clarify the drawings for the Foreman in the field. We also have a "Trimble" robot that works off of radio signal, and uses a tripod mounted laser transit to plot the exact location of conduit stub-ups, homerun boxes, underground ductbanks, site lighting, conduit and cable tray racks (layed out on decks above and installed anchors to suspend the all-thread for the racks below prior to the concrete pour). We also work in conjunction with a Pre-Fab shop to route as much work through them (in a controlled envirnoment)and then sent out to the jobs. This includes wire, cable, mc, conduit bends, pre-fabbed concrete boxes, fixture whips, support brackets for can lights, etc.
If the foreman that is running the job follows the Pre-Plan prints (colored and circuited in the correct color) that we give them, then they end up with a compelete "As-built" job before they set foot on site. We are also in charge of submitting "shop drawings" for electric rooms, necessary circuitry, MEP coordination drawings, RFIs, etc.

Sounds like a lot of stuff to do, but the Foreman in the field love it. They continue to ask for more. We can recognize problems (in Pre-Planning)and in most cases reslove the issues before the Foreman ever sees them (although they are made aware of the changes), especially with the MEP coordination.

We didn't invent Pre-Planning...it is being done all over the country with outstanding results. This is the product of incomplete Engineering, poor drawings, and the multitude of questions (RFIs) that we encounter nowadays. The last big job that we did had over 1100 RFIs (not all electrical) 12 ASIs, and 110 CCDs. (this job was not pre-planned)

In the defense of the Engineers...they are doing all that they can to engineer jobs considering the time constraits, and budgets, codes, ordinances, etc. they we are forced to comply with in this day and age. It all boils down to the cost of money. The invester wants an imediate return on his money. Get it Engineered, get it built, and get it on-line as fast as possible.
 

ohm

Senior Member
Location
Birmingham, AL
A Pre-planner is a person (usually comes from the field, Foreman, General Foreman, Super.) that takes a job that is under contract, or has a letter of intent and using AutoCAD lays out the service, underground, slabs, walls, overhead, cabletray, conduit racks, lighting (lighting controllers) special systems, fire alarm, creates panels schedules based on the pre-plan, temporary layout, etc. Anything that is needed to clarify the drawings for the Foreman in the field. We also have a "Trimble" robot that works off of radio signal, and uses a tripod mounted laser transit to plot the exact location of conduit stub-ups, homerun boxes, underground ductbanks, site lighting, conduit and cable tray racks (layed out on decks above and installed anchors to suspend the all-thread for the racks below prior to the concrete pour). We also work in conjunction with a Pre-Fab shop to route as much work through them (in a controlled envirnoment)and then sent out to the jobs. This includes wire, cable, mc, conduit bends, pre-fabbed concrete boxes, fixture whips, support brackets for can lights, etc.
If the foreman that is running the job follows the Pre-Plan prints (colored and circuited in the correct color) that we give them, then they end up with a compelete "As-built" job before they set foot on site. We are also in charge of submitting "shop drawings" for electric rooms, necessary circuitry, MEP coordination drawings, RFIs, etc.

Sounds like a lot of stuff to do, but the Foreman in the field love it. They continue to ask for more. We can recognize problems (in Pre-Planning)and in most cases reslove the issues before the Foreman ever sees them (although they are made aware of the changes), especially with the MEP coordination.

We didn't invent Pre-Planning...it is being done all over the country with outstanding results. This is the product of incomplete Engineering, poor drawings, and the multitude of questions (RFIs) that we encounter nowadays. The last big job that we did had over 1100 RFIs (not all electrical) 12 ASIs, and 110 CCDs. (this job was not pre-planned)

In the defense of the Engineers...they are doing all that they can to engineer jobs considering the time constraits, and budgets, codes, ordinances, etc. they we are forced to comply with in this day and age. It all boils down to the cost of money. The invester wants an imediate return on his money. Get it Engineered, get it built, and get it on-line as fast as possible.

Cool, sounds like you guys earn your keep!
 

Mr. Wizard

Senior Member
Location
Texas
A Pre-planner is a person (usually comes from the field, Foreman, General Foreman, Super.) that takes a job that is under contract, or has a letter of intent and using AutoCAD lays out the service, underground, slabs, walls, overhead, cabletray, conduit racks, lighting (lighting controllers) special systems, fire alarm, creates panels schedules based on the pre-plan, temporary layout, etc. Anything that is needed to clarify the drawings for the Foreman in the field. We also have a "Trimble" robot that works off of radio signal, and uses a tripod mounted laser transit to plot the exact location of conduit stub-ups, homerun boxes, underground ductbanks, site lighting, conduit and cable tray racks (layed out on decks above and installed anchors to suspend the all-thread for the racks below prior to the concrete pour). We also work in conjunction with a Pre-Fab shop to route as much work through them (in a controlled envirnoment)and then sent out to the jobs. This includes wire, cable, mc, conduit bends, pre-fabbed concrete boxes, fixture whips, support brackets for can lights, etc.
If the foreman that is running the job follows the Pre-Plan prints (colored and circuited in the correct color) that we give them, then they end up with a compelete "As-built" job before they set foot on site. We are also in charge of submitting "shop drawings" for electric rooms, necessary circuitry, MEP coordination drawings, RFIs, etc.

Sounds like a lot of stuff to do, but the Foreman in the field love it. They continue to ask for more. We can recognize problems (in Pre-Planning)and in most cases reslove the issues before the Foreman ever sees them (although they are made aware of the changes), especially with the MEP coordination.

We didn't invent Pre-Planning...it is being done all over the country with outstanding results. This is the product of incomplete Engineering, poor drawings, and the multitude of questions (RFIs) that we encounter nowadays. The last big job that we did had over 1100 RFIs (not all electrical) 12 ASIs, and 110 CCDs. (this job was not pre-planned)

In the defense of the Engineers...they are doing all that they can to engineer jobs considering the time constraits, and budgets, codes, ordinances, etc. they we are forced to comply with in this day and age. It all boils down to the cost of money. The invester wants an imediate return on his money. Get it Engineered, get it built, and get it on-line as fast as possible.

What part of the world are you in?
 

GUNNING

Senior Member
?

?

That sounds way cool. Im trying to imagine the redneck foreman trying to coordinate his conduit bends and hangers with the dumb as a stump sledge hammer mechanic. Then the thought of a well thought out job easily laid out and preplanned like it was out of a kit, now that would be fun. What part of the world and what type of projects?
 

Natfuelbilll

Senior Member
Where in the gear torque specs or in the torque wrench instructions does it say:

'Torque, shake, repeat?':-?

I have seen some electricians "seat" the wire during tightening.

More as a method than as a step by step.

Is there a benefit?

....I wonder what the IR thermographers have seen....
 

hardworkingstiff

Senior Member
Location
Wilmington, NC
Where in the gear torque specs or in the torque wrench instructions does it say:

'Torque, shake, repeat?':-?

Good question Chris. I am curious though, if the inspector "shakes" it and it feel loose, ......... ?

I've also torqued, "shaked", then checked it with a torque wrench to find the connection very loose. I'm not comfortable with leaving a connection without some shaking, but I'm also concerned I'm doing things I shouldn't.
 

electricmanscott

Senior Member
Location
Boston, MA
1. We do. Especially since our inspector checks connections by wiggling the wires to see if they'll pull out. It's happened more than once....

The inspector should not be doing that. If you tighten and leave alone it will likely be fine. Once you start wiggling it WILL losen up a bit. Does he retighten when he's done?
 