FYI, Square D torgue response

FYI, Square D torgue response

Where in the gear torque specs or in the torque wrench instructions does it say:

'Torque, shake, repeat?':-?

I called the Square D rep today and told him I was installing two 4/0 cables in a lug on a 400-amp breaker. I told him I have been in discussions with other electricians on what the proper way to tighten the conductors is. I told him some electricians say torgue it and leave it, and others (including me) torgue it to the spec, wiggle the conductors about an inch to an inch and a half in all directions then torque it again, repeat until the torgue setting holds after the "wiggling".

I asked him what the proper methodology would be for tightening the lug on this breaker (the lug is rated for 2 conductors up to 250 kcmil).

Here is his response:

Lou,
I talked to our breaker application engineer & he said what you are doing is a good practice.
There is nothing in writing in our instructions, but it makes practical sense to retighten
these lugs.
There is more chance for the conductors to " spead out & settle in" when using 2 conductors.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
One more thing. If I wiggle and retorque the parallels, now I have to retorque the mains connections to the buss due to the fact that the shaking has compromised that connecioin also. Sounds like work I don't have time to do.
 

hardworkingstiff

Senior Member
Location
Wilmington, NC
One more thing. If I wiggle and retorque the parallels, now I have to retorque the mains connections to the buss due to the fact that the shaking has compromised that connecioin also. Sounds like work I don't have time to do.

Fact? That's a strong word.

The breaker I was using is in an enclosure with line and load conductors. Most of the 400-amp breakers I use are either I-Line or bolted to the buss and shaking the conductors would not loosen that bolted connection. You must be talking about something I've not had experience with.
 

Natfuelbilll

Senior Member
Question 2.........
Have you ever used a torque wrench to measure your efforts?

I am not 100% sure that all manufacturers termination provide a spec for tightness, I would bet most do, and where they do is it then a Code violation to NOT use a torque measuring device?
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
and where they do is it then a Code violation to NOT use a torque measuring device?

I doubt you will get a red-tag for not using a torque wrench, but IMO it is implied.

110.14

FPN: Many terminations and equipment are marked with a tightening torque.
Handbook commentary following 110.14.

Section 110.3(B) applies where terminations and equipment are marked with tightening torques.
 

Mr. Wizard

Senior Member
Location
Texas
Austin Texas is the nearest big city, our headquarters are in Manor (pronounced May-nor) just East of Austin. We have small shops in Dallas, Houston, and in the Valley (Down South). We also have a small office in San Antonio.

I know exactly where Manor is located. I heard that work is booming in Austin, but I heard that two or three months ago. It seems everytime I drive into Austin I see several high-rise cranes west of I-35 , near UTA.
 