ok please learn me here I always thought 208v was on a stinger leg Y style with the middle point going to ground . Why or how do you get 208 on two legs wouldnt that be 240v? Thanks in advance
What frenchy said was correct. It's a 120/208 3-phase service. I'm going to go with a 208v 2 circuit SPST electronic timeclock, 208v rated coil and an electrically held 8 pole contactor. Any objections?
 
Any objections?
Honestly? There's no advantage to using 208 instead of 120 (except easier troubleshooting in the future, perhaps), and a couple of disadvantages: the timer might cost more, and the 2p breaker definitely will.

Your loads will still be supplied by four 2p breakers, obviously.
 
Honestly? There's no advantage to using 208 instead of 120 (except easier troubleshooting in the future, perhaps), and a couple of disadvantages: the timer might cost more, and the 2p breaker definitely will.

Your loads will still be supplied by four 2p breakers, obviously.

This is a change order and i'm trying to keep the price at a minimum for the customer. I can use one of the existing 2-pole breakers powering the lights to also power the time clock.
 