The age old question. My instructor says never to backstab, but on externship last week the contractors swear by it. Which is the most efficient, safe, and correct way to wire a receptacle or switch.
Screwless terminal connectors of the conductor push-in type (also known as "push-in-terminals") are restricted to 15 A branch circuits and are for connection with 14 AWG solid copper wire only. They are not intended for use with aluminum or copper-clad aluminum wire, 14 AWG stranded copper wire, or 12 AWG solid or stranded copper wire.
Single and duplex receptacles rated 15 and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors have been investigated to feed branch circuit conductors connected to other outlets on a multi-outlet branch circuit, as follows:
Back wire (screw actuated clamp type) terminations with multiple wire access holes used concurrently to terminate more than one conductor
Side wire (binding screw) terminals used concurrently with their respective push-in (screwless) terminations to terminate more than one conductor
Not! Back-wired, absolutely! Better than screws.Lithium1994 said:To backstab or not to backstab?
I do use those; the load is only more lights.bikeindy said:I wonder if anyone who won't backstab will use stab type "wirenuts"? do you remove them from can fixtures when you wire them?
It's okay as long as you don't get back-wired! :shock:charlie b said:I've been backstabbed. Does that count? :lol:
bphgravity said:As far as UL is concerned, "backstabbing" is completely fine:
Screwless terminal connectors of the conductor push-in type (also known as "push-in-terminals") are restricted to 15 A branch circuits and are for connection with 14 AWG solid copper wire only.
celtic said:bphgravity said:As far as UL is concerned, "backstabbing" is completely fine:
Screwless terminal connectors of the conductor push-in type (also known as "push-in-terminals") are restricted to 15 A branch circuits and are for connection with 14 AWG solid copper wire only.
Do you have a UL link for this?