I know this topic has been beat to death but I cant find a reference to my situation. This was installed in the 1970s
I have 4 4x4 posts fed from a nearby building. Each post has 2 20 amp circuit breakers and 2 GFI receptacles. The feeder from the building goes to the first post then loops to each of the other posts. There was no equipment ground installed with the feeders. There are no ground rods or any type of ground system. On the back of the first 2 posts is a galvanized water pipe that goes to the same building as the feeders. My question is, can I use this water pipe as the grounding electrode, and if so, does the grounding electrode conductor bond to the grounded (neutral) bar? Also if I run a GEC from the 2nd post to the 3rd and 4th posts, do these need to be bonded to the neutral bar.