ffishbait said:Everything in the 100 amp garage panel is less than 6 swipes. I don't know what the HO future plans are, but everything I'm hooking up; outlets, lights, welder, and saw is less than 6.
I understand that the panel needs a disconnect, I didn't realize that it needs to be on the outside of the garage. It was a step I did not anticipate.
Thanks to all that posted comments.
ffish
It doesn't need to be outside of the garage. This is where the inspector is wrong. It needs to be at the nearest entry of the feeder conductors. A panelboard with a main CB will be compliant.