I've allready asked one member this question but I'll throw it out to the world as well.
I recently had a contractor ask me to wire a 2500 sq.' cabin. without really thinking I went ahead and threw a 200 A. meter/ main and, a 200 A. 30/40 subpanel on. two weeks later when I went to rough the place in, he had 11 240v. wall heaters he wanted to install. Anyway by the time I had all my home runs pulled I came up with too many wires for the allowable 30 spaces.
My question is this would it be considered poor practice to instal 4 piggyback breakers to free up the space I need in the subpanel? or do I need to tear out the subpanel and feeders and put in a 40/40 panel.

(I know what you guys are thinking...."Dumb Rookie")

Dana
 
solaeros said:
I've allready asked one member this question but I'll throw it out to the world as well.
I recently had a contractor ask me to wire a 2500 sq.' cabin. without really thinking I went ahead and threw a 200 A. meter/ main and, a 200 A. 30/40 subpanel on. two weeks later when I went to rough the place in, he had 11 240v. wall heaters he wanted to install. Anyway by the time I had all my home runs pulled I came up with too many wires for the allowable 30 spaces.
My question is this would it be considered poor practice to instal 4 piggyback breakers to free up the space I need in the subpanel? or do I need to tear out the subpanel and feeders and put in a 40/40 panel.

(I know what you guys are thinking...."Dumb Rookie")

Dana
A 30/40 panel means 30 position 40 circuits so your allowed to put in 10 piggybacks. IMO. So speaking you'll get no more circuits with a 40/40 then you will with a 30/40.;)
 
It's a 30/40 panel, so what's the problem with tandems? Nothing that I can see. Too bad you got caught with your pants down this time. Better luck on the next job.
 
If the panel is rated for more than 30 breakers (i.e. a 30/40), than you would be foolish to rip it out and install a new one.
 
stickboy1375 said:
Your allowed 42 OCD in each cabinet...I don't have a problem with twin breakers as long as your not over the limit...
I have a problem with tandems in a panel not rated for tandems. I see non CTL "cheater" tandems in panels every day that were never rated for tandems. They're not over the 42, but they're not rated for tandems either.
 
stickboy1375 said:
Your allowed 42 OCD in each cabinet...I don't have a problem with twin breakers as long as your not over the limit...

The panel would have to be rated as a panel that accepts tandems to 42 OCPD.12/24. 30/40 etc..dont think I`ve seem a 30/42.
 
My next question would be if there are 11 240 volt heaters I would question the load calc on the residence.What is the total load calc going to be.If using nothing but electric heat then i would doubt that there would be gas stove/cook top. wall ovens etc.You might want to look at that aspect.Then decide if there needs to be a change order given.KACHING !!!!!!!
 
stickboy1375 said:
The only time I see tandems installed is when the last guy didnt want to install a sub-panel....
Eh, I dunno. I often want to. More often, I am not permitted to by the property owner. I always present the tandem option if it's permissable. Let them make a fully informed decision.
 
mdshunk said:
Oh, shame shame. I'm betting that the neutral/ground bar in those panels is screaming for mercy too.

Yep... and some guys are not good at making up panels... its funny how I never struggle when I go back to a panel I did, but WOW it takes forever with someone elses....
 
stickboy1375 said:
Yep... and some guys are not good at making up panels... its funny how I never struggle when I go back to a panel I did, but WOW it takes forever with someone elses....

There's allready a subpanel, it's just a standard "homeline" panel, yes it's rated for tandems, i'm just questioning wether or not it would be seen as poor worksmanship on a new residence
 
solaeros said:
... i'm just questioning wether or not it would be seen as poor worksmanship on a new residence

If you planned all along to use tandems, maybe so. You kinda got blindsided, so your pre-planning in using a 30/40 panel paid off. This is among the reasons why you plan with a little wiggle room, in case things like this crop up. Don't sweat it.

(All that electric heat, though... how's your demand load calc look now?)
 
solaeros said:
I recently had a contractor ask me to wire a 2500 sq.' cabin. without really thinking I went ahead and threw a 200 A. meter/ main and, a 200 A. 30/40 subpanel on. two weeks later when I went to rough the place in, he had 11 240v. wall heaters he wanted to install. Anyway by the time I had all my home runs pulled I came up with too many wires for the allowable 30 spaces.
Two thoughts:

A) You should always discuss the expected load before deciding anything else, as you have discovered.

2) You don't need separate circuits for each heater; split them up evenly, with 3840 watts as a limit per circuit.*

D) I have no problem with properly-used tandems, even in new work. I always start with the lowest-current breakers first.


As Allen mentioned, what is the total heater load wattage? You may have a non-issue.

*If the load can be considered non-continuous, you can go to the full 4800 watts per circuit.


mdshunk said:
Oh, shame shame. I'm betting that the neutral/ground bar in those panels is screaming for mercy too.
Not necessarily; line-to-line loads don't affect the neutral bar, and multiple EGC buses can be added relatively easily.
 
solaeros said:
There's allready a subpanel, it's just a standard "homeline" panel, yes it's rated for tandems, i'm just questioning wether or not it would be seen as poor worksmanship on a new residence

I know a few EIs who "frown" on tandems in new work.

As to whether it's "poor workmanship" - beauty is in the eye of the beholder...and who be holdin' the final payment :)
 
LarryFine said:
Not necessarily; line-to-line loads don't affect the neutral bar, and multiple EGC buses can be added relatively easily.
Yeah, but do you really think that the knucklehead who took the panel over 42 circuits bothered to put in another ground bar? Very seldom in these non-compliant panels. Plus, when they're that full, they often have some age on them. Older panels had notoriously small neutral/ground bars. If you see a panel with more than 42 circuits, you're more than likely also looking at a panel with double and tripled up ground buss holes.
 
The tandem CBs are fine. I never PLAN to use 'em and end up using "em alot. The thing that is most important to me is the actual load on the panelboard. I tend to use quite a few lightly loaded circuits rather than very few heavily loaded ones. At the end of the day, though, who really cares?
 