Cow
Senior Member
- Location
 - Eastern Oregon
 
- Occupation
 - Electrician
 
I was having a discussion with a coworker about a project he's on.  He's adding a 500 amp fused disconnect fed from a  2000 amp main breakered switchboard.  He ran two 2 1/2" emt conduits between the switchboard and disconnect thinking he'd run parallel 250's tapping after the main.  When he realized his wire length at 23' put him into needing 1/3 ampacity for the tap(667 amps) requiring parallel 400's, the emt conduit is too small.  I mentioned if he could tap the 2000 amp buss ahead of the main, there were no tap rule requirements.  
Our we reading the code correctly? A tap after the main requires 667 amps of conductor, a tap before the main requires running just 500 amps of conductor? I can't find the logic in tapping before the main and having no main OCPD but getting away with smaller conductor?
Thoughts?
	
		
			
		
		
	
				
			Our we reading the code correctly? A tap after the main requires 667 amps of conductor, a tap before the main requires running just 500 amps of conductor? I can't find the logic in tapping before the main and having no main OCPD but getting away with smaller conductor?
Thoughts?
				