OK, here's the AC / lighting issue: The owner had it all screwed up in his head.
He noticed the furnace was blowing air, but not cold air. So he checked the breaker. It was tripped. He reset it, and it tripped the breaker feeding the subpanel that had the AC breaker in it. This killed the entire subpanel which had that side of the building's lights in it. We tried resetting it, but it tripped immediately. I crawled up on the roof and took the cover off the compressor. There was a boost capacitor added. So my guess is it was toast and that's what is causing the breaker to trip.... too much current trying to start the compressor.
So we had the owner contact his HVAC guy. But we still have the glow-in-the-dark wiring to deal with.
The POCO arrives and finds the noodle splice at both the weatherhead and at the transformers out on the pole were not correct. It appeared they weren't crimped far enough and we could see burn marks on them. So those were replaced by the POCO.
But we still had arcing after that.