Did you find/solve the problem and want us to figure it out?
Or are you still working on it?
Why is this a question that always gets asked?
Did you find/solve the problem and want us to figure it out?
Or are you still working on it?
Why is this a question that always gets asked?
Maybe because we want to know. You never said if you solved it or not.
Question.. bear with me ... but if no arc when main turned off, wouldn’t that rule this idea out? I mean, unless a main conductor has burned as well, so that when it gets warm enough through needs it then arc itself to the conduit? I know that can happen but have not seen it happen in real life so do not know if it would be like video...I can't think of anything that hasn't been ruled out except...
-Open neutral between the meter and the main panel (causing the neutral current to return to the neutral bonded at/near the meter via the conduit instead of the conductor).
-Some jury-rigged neutral or EGC creating a path back to the nipple we see in the video.
480sparky, can you at least confirm if your friend with the IR camera helped you find the issue?
I changed my mind. The problem is too much inductance.
I can't think of anything that hasn't been ruled out except...
-Open neutral between the meter and the main panel (causing the neutral current to return to the neutral bonded at/near the meter via the conduit instead of the conductor).
-Some jury-rigged neutral or EGC creating a path back to the nipple we see in the video.
480sparky, can you at least confirm if your friend with the IR camera helped you find the issue?
Where do ducks sleep at night?
Inductance....:lol:
Yes, but did you tighten the locknut ...
Yes, but did you tighten the locknut ...
Look closely, looks to me like an offset nipple is threaded into a coupling at the end of the raceway run.EMT to a die cast set screw connector, coupling, then a die cast offset nip. Coupling doesn't look right, looks too big (thick) for steel threaded. Looks like it could be a PVC coupling.
THW conductors with the fiber bushing is old school, like 1960's or before. Die cast fittings are, I am guessing, from a later era. So the panel was taken apart and moved a little then put back reusing old parts (?).
Is the coupling PVC slipped over the EMT set screw connector, so they could neatly join to the die cast offset nip (?). I don't see the fourth THW, the neutral, but assuming it is there and bonded to the can. So they damaged the THW when they took it apart and put it back together and it is faulting to the offset nip, and since the coupling is (maybe) PVC there's no useful N to G bond at the meter socket and it has to flow through the loose locknut to the panel bonding screw (???).
That is still a neutral connection issue and was an answer long ago, I have seen that happen this way before, as well as seen loose connection between different bars of the neutral assembly. One doesn't always catch such things while there is something glowing, but there is often signs of overheating or at least some arcing indication.The IR photos helped narrow it down, although he hasn't sent me copies of the images yet. But we noticed there were no GECs into the panel, either to any rods or pipes. There was, however, a single rod right below the panel (yes, indoors!), so while I was landing a #4 bare on the neutral bar, I noticed some arcing between the neutral lug and the bus for the neutral bars.
A loose neutral was my first impression, so I had originally tugged on it to see if the lug needed tightened. Turns out the lug itself was tight on the conductor, but not to the bus. So I turned off the main and pulled the neutral conductor out of the lug. By pure luck, the lug was bolted to the bus with a slotted bolt that was easily accessible through the lug. A good crank (about 1/8 turn) and relanding the neutral wire solved the arcing locknut.
Used to be common to mark the high leg with red, and often was on the right position instead of center position. POCO's meter needed high leg to be on right position to work properly is part of reasoning.Yes, the red leg delta was odd also. Was it?, 240 V line to line?. With the reg leg delta and single phase loads, you can only load up to something like 50% of the kVA rating of the transformer.
You are really limited in loading up the red leg delta unless you have mostly 3 phase loads.